I just got my machine and am in the process of setting up a 230v outlet in my garage. In the manual in the section "Power Sources - Input Voltage and Current" it states for 230, Max amps at 27 amps. So I went to HD and got a 2 pole 30 amp breaker, and already have plenty of 10 gauge wire.
Looking at the manual again, I saw another section I didn't notice earlier "Power Sources - Recommended Input Wire & Fuse Sizes" here it lists 12 gauge wire and a 40 amp breaker.
I have seen many posts on GJ showing many guys running 200-210 welders using 30 amp breaker, usually with a 50 receptacle labeled 30 amp for welder only.
Should I go with my first intention which was 10 awg wire with 30 amp breaker and it should work fine? Worst case scenario being the breaker goes off too often and I go buy a 40 amp?
Looking at the manual again, I saw another section I didn't notice earlier "Power Sources - Recommended Input Wire & Fuse Sizes" here it lists 12 gauge wire and a 40 amp breaker.
I have seen many posts on GJ showing many guys running 200-210 welders using 30 amp breaker, usually with a 50 receptacle labeled 30 amp for welder only.
Should I go with my first intention which was 10 awg wire with 30 amp breaker and it should work fine? Worst case scenario being the breaker goes off too often and I go buy a 40 amp?