Towards a KISS design, has anyone used a line voltage thermostat to control their circulation pump for a single zone / garage radiant system? The more common option is a pump controller wired to a low voltage thermostat.

The thermostats have an inductive/motor rating, so in theory it seems that they should work fine. Not sure if it would suffice to allow the circuit breaker to protect any pump short/overload, or if another fuse should be incorporated.
 
To avoid these ads, REGISTER NOW!

budmur

Well-known member
Joined
Jul 21, 2014
Messages
70
Location
Athens, TN
As long as the pump is within the thermostat's voltage and current ratings, and the pump has internal thermal protection it should be fine.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
The pump is an inductive load, line voltage heating is a resistive load. Make sure the thermostat's contacts have rating for the inductive load. (I believe it will...)

Personally I'd use a standard thermostat with a transformer and relay.
 
To avoid these ads, REGISTER NOW!

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
I've seen it done before here and wired mine to work that way. Then use a water heater/boiler that has it's own thermostat to maintain water temperature. Some of the boilers seem to also have a control for the pump built in so you trigger the boiler with a low voltage stat and then the boiler turns on the system.
 

jlckmj

Well-known member
Joined
Dec 7, 2009
Messages
732
Location
SE Wiscosin
I use exactly that, a line voltage thermostat wired directly into the pump.
It has worked perfectly for years.

Jim
 
OP
C

Crazy68Dart

Well-known member
Joined
Apr 10, 2010
Messages
484
Location
NE Ohio
I use exactly that, a line voltage thermostat wired directly into the pump.
It has worked perfectly for years.

Jim

What is your setup? Boiler, conventional or on-demand water heater? How far away is the thermostat from your mechanical (water heater, plumbing, pump, etc?)
 