liquidtight conduit to AC Length

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
The panel is about 8 foot from where I want to place the mini split, because it is in sight there is no disconnect, can I run the liquid tight conduit (same stuff that made the 6 foot long whips) and run 8-9 feet to the air conditioner?

THIS
http://www.homedepot.com/p/AFC-Cabl...gclsrc=aw.ds&dclid=CM6e0JWhqNYCFUvBZAoddyMJZA

My understanding is that as long as it is supported/ mounted less than 12" from the panel/box and then mounted less than every 36" there is no restrictions on the length of these conduits.
 
To avoid these ads, REGISTER NOW!

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,674
Location
Maine
Yes, not sure on the 3/8 though. I've never seen 3/8 liquid tite

Sent from my SM-G950U using Tapatalk
 

Wirepuller

Banned
Joined
Oct 6, 2014
Messages
305
Liquid tite looks bad. Emt, compression fittings and a rigid coupling and transition to liquid tite close to the unit.


Sent from my iPhone using Tapatalk
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
Liquid tite looks bad. Emt,RAINTITE compression fittings and a rigid coupling and transition to liquid tite close to the unit.


Sent from my iPhone using Tapatalk


Compression fittings must be listed as raintite in order to be used outdoors, plain old compression is a premium indoor fitting.
 
To avoid these ads, REGISTER NOW!

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
How do you guys feel about the non-metallic liquidtite versus the stuff with the metallic liquidtite? I always use the metallic, rationalizing it that it is subject to abuse just by virtue of people walking around it, landscapers, etc.

Thoughts?
 

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
There is this in some codes:
Liquid-tight flexible nonmetallic conduit without integral reinforcement within the conduit wall shall not exceed 6 feet in length.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
How do you guys feel about the non-metallic liquidtite versus the stuff with the metallic liquidtite? I always use the metallic, rationalizing it that it is subject to abuse just by virtue of people walking around it, landscapers, etc.

Thoughts?

I like the NM sealtite over the metallic sealtite as it's easier to use & takes abuse better.
 