Load Center\Electrical Panel Mounting in Pole Barn

DeerePower

New member
Joined
Dec 22, 2014
Messages
2
Hi All,

Recently put up a 40x56 pole barn in Iowa. Currently working on getting power to the shop sub-feed from house with 100 amp service. I've completed the trenching and have a 2" conduit entering the building from below grade. I have added 2x6" girts on the inside of the post (similar to the girts on the outside of the post to which the steel is fastened) which i plan to hang a large 3/4" peice of plywood to mount the load center. I went this way in case i plan to insulate in the future. My question, what is the cleanest way to route wiring from the load center to lights, outlets, etc? Simply come off the plywood and run behind the post on top of girts or up the side of posts to light fixtures? Any pics of your setup would be appreciated.
 
To avoid these ads, REGISTER NOW!

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,293
Location
Mt Rainier foothills, WA
Hi All,

Recently put up a 40x56 pole barn in Iowa. Currently working on getting power to the shop sub-feed from house with 100 amp service. I've completed the trenching and have a 2" conduit entering the building from below grade. I have added 2x6" girts on the inside of the post (similar to the girts on the outside of the post to which the steel is fastened) which i plan to hang a large 3/4" peice of plywood to mount the load center. I went this way in case i plan to insulate in the future. My question, what is the cleanest way to route wiring from the load center to lights, outlets, etc? Simply come off the plywood and run behind the post on top of girts or up the side of posts to light fixtures? Any pics of your setup would be appreciated.

Flush mount your panel inside your new wall. Run the wires up out of the top of the panel to the attic within the wall as you would any regular wall.

Here's mine. Sure you will lose some insulation depth at the actual panel but keeping your wires safe in the wall is desirable.

Here's mine in my pole barn.
 

Attachments

  • IMAG0833.jpg
    IMAG0833.jpg
    112.1 KB · Views: 165
  • IMAG0834.jpg
    IMAG0834.jpg
    104.4 KB · Views: 138
  • IMG_0211.jpg
    IMG_0211.jpg
    145 KB · Views: 134
  • IMAG0548.jpg
    IMAG0548.jpg
    95.6 KB · Views: 135
OP
D

DeerePower

New member
Joined
Dec 22, 2014
Messages
2
Highbeam,

Thanks for the reply and pictures. Very nice shop. How did the cost compare on stud walls and OSB compared to tin? If I do insulate down the road, I was thinking of using 8ft blanket style insulation and ribbed tin. Interested in hearing other options, anyone else have their experience to share?
 
To avoid these ads, REGISTER NOW!

thewatusi

Well-known member
Joined
Dec 27, 2013
Messages
1,256
Location
Philly Burbs
Hi All,

Recently put up a 40x56 pole barn in Iowa. Currently working on getting power to the shop sub-feed from house with 100 amp service. I've completed the trenching and have a 2" conduit entering the building from below grade. I have added 2x6" girts on the inside of the post (similar to the girts on the outside of the post to which the steel is fastened) which i plan to hang a large 3/4" peice of plywood to mount the load center. I went this way in case i plan to insulate in the future. My question, what is the cleanest way to route wiring from the load center to lights, outlets, etc? Simply come off the plywood and run behind the post on top of girts or up the side of posts to light fixtures? Any pics of your setup would be appreciated.

conduit

EMT41.jpg

random web pic
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,669
Location
SE MI
My question, what is the cleanest way to route wiring from the load center to lights, outlets, etc? Simply come off the plywood and run behind the post on top of girts or up the side of posts to light fixtures?
That is not allowed in a residential building. Must be conduit up to the height of the ceiling, even if there is no ceiling ! Conduit must be secured. Romex must secured within code limit of exiting the conduit. Individual wires must always be in conduit.
 