The 100 amp at the top of the breaker is the main. I don't know how much I like this design as I was expecting a dedicated breaker where there would be main lugs. I was going to go with the Square D QO 100a panel, but the rear knockouts weren't large enough for 2" and I wasn't very found of the stacked neutral/ground bars. I also wasn't a too found of all of the plastic.This is actually a very nice panel, heavier than the same size Square D and is a copper bus.
This will be a sub-panel. The neutral and ground bars will not be bonded. I have a few options on how to run this.
-I can leave it the way it is without the bond bar and have neutral only on one side while picking up a ground bar kit from Lowes.
-I can put the bond bar back without the little bracket that actually bonds both bars, screw it back into the panel and I will have a ground on one side and a neutral on the other. Not sure how much I like this idea as I would prefer to minimize connections.
-I can pick up a ground bar kit, put that on one side and then run a jumper wire going from one neutral bar to the other neutral bar. I would have neutral bars on both sides while only having ground on one side.
-Finally, I can try and locate the insulated aluminum bar that comes on the larger Eaton panels to connect both neutral bars. Then I can buy a ground bar kit and would have neutral on both sides and ground on the other. I like this option the best as its most factory.
Only real questions I have are which one would be best as far as making wiring simpler and if I pick up two ground bar kits, will the screws that are used to mount it be enough to connect both bars or would I need to run jumper wire from one to the other? I have only seen panels with one ground bar kit and I only have one wire coming in so not sure what would be the preferred way to have two.
BTW, I am in Goldsboro, NC and will be doing the wiring myself. It will be "inspected" by an electrician once done. We are on NEC2011.