Long water line

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,391
Location
Texas
Good morning,

I’ve got a long water line to run from the road to my cabin. 600-700’.

Up till now, I‘ve done fine with my 5/8 garden hoses but it’s time to trench and put in pipe. Not many fixtures. Kitchen sink, toilet, bathroom.

2” is probably still too small but it’s about all I can afford.

PEX is doable but very expensive at that size.

I’m looking at HDPE (polyethylene).

One of my questions is can I use compression fittings or barbs with HDPE? I’d rather not get into fusing/melting the fittings. Seems like that is going to cause issues later in terms of repairability. Or is that the way to go?

My other question is which HDPE am I looking for? I vaguely understand there is minicipal quality that is heavier and ’once and done.” But not finding actual specs. I don’t want to have to dig this up later.

Any thoughts on how best to get this job done appreciated.

Thanks

 
To avoid these ads, REGISTER NOW!

jack stand

Well-known member
Joined
Feb 29, 2012
Messages
3,413
Location
Lakes Region Maine
Attention to your backfilling technique and material is a bigger factor for longevity. 2" pipe also seems more than you can use from your description.
If you put a marker (pipe,etc.) at all the connections that could be helpful in the future.
 

sjvicker

Well-known member
Joined
Aug 9, 2014
Messages
610
Location
SW Washington
I run 1-1/4" HDPE from my cistern 700' down a hill to my future build site. It generally comes in different pressure ratings (100psi, 160psi, 200psi). From what I found 100psi is garbage, 160psi is acceptable and 200psi is the top of the line. I ran 160psi line that I purchased from home depot.

I messed around with the expensive compression fittings and at the end of the day just used the plastic barbs with two high quality stainless hose clamps on each side of the barb.

Use a propane torch to heat the pipe slightly (dont get it too hot) and the barbs go in easier.
 

Hooked

Well-known member
Joined
Sep 24, 2010
Messages
480
Location
League City, Texas
I ran 3/4" PVC 350' to our house over 40 years ago and it serves us well. Another 300' further to the barn with plenty of water/pressure. Have added water lines to greenhouse, boat shed and workshop as well with no issues. The only time I've had to repair any lines is due to freezing.
For a cabin 1" is more than enough.
 

Fav Onefour

Well-known member
Joined
Jul 14, 2022
Messages
778
Location
MN cold and hot
No need to use 2" line unless you are planning on the pipe being your tank. That will be a lot of water just sitting in pipe and a lot of money exiting your wallet.
How deep do you run water lines in your area? We bury deep around here and use plastic barb fittings with stainless clamps. We do make sure the trench lay is good when we back fill. The first layer on top is done with shovels and labor.
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,391
Location
Texas
Thanks guys. The real world stuff helps.

No frost line here. 6” min but 12” is good practice. No authority having jurisdiction. Don’t want trouble in future and will probably do 12”.

It looks like I can run HDPE with barbs. I like having that option given how cheap it is by comparison.

Vague plan is to run 200’ sections then stub it up with a T and a hose bib in a vault.

I’ll put a larger vault near the cabin and go with pex and sharkbite from there. Or maybe pex A if I can get or rent a cheap tool.
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,391
Location
Texas
Yes. Having hose bibs will help with watering pecan trees. Dragging 200’ of hose around is a pain. I” pex is ok. 2” gets up there.
 
To avoid these ads, REGISTER NOW!

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
3,033
Location
Peace Valley,mo
Height of rise of the water line. 2.31' per lb doesn't matter what size pipe
231' =100 lbs at the bottom
1 foot of water creates 0.433 psi of pressure
 
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,391
Location
Texas
The idea of a smaller line and tank at the cabin is definitely on the table. Either a larger rainwater deal that would be topped off with a float valve or a smaller tank inside.
 

jrsavoie

Well-known member
Joined
Jun 4, 2013
Messages
1,510
Location
North east Illinois
By the time the water line needs to be changed, the outer pipe will likely be filled with roots
It gives me something to hit when digging. We go 4' deep here. Root infiltration isn't such a deal below the clay level.

In areas where we worry about root issues, we use unslotted tile or sometimes pvc.

The black plastic water lines don't need to be changed often. The line running about 100 yards to the tool shed is over 50 years old.

If it leaks we don't notice. We did notice when the bottom of the hydrant rotted off. Had a puddle in a dry spell.

That's when I decided an indicator light to be on when the pumps running would be a good idea.

The only reasons we've ever had to change stuff was something getting hit by the digger or change of plans.

I've never actually seen the black plastic water line fail.

We have used the tile to pull other stuff through in addition to the water line. Air line from the compressor and telephone lines, back in the days of land lines.

We always left a pull wire inside the tile.
 
Last edited:

Skooterj

Well-known member
Joined
Mar 11, 2021
Messages
760
Location
Indiana
1" or 1 1/4" , 160 PSI HDPE in the longest roll you can source should be more than enough. Barb fittings work great, just use two clamps on each side. I prefer stainless or brass barbs. Plastic barbs are cheaper, but can crack if you overtighten the clamps.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
12,085
Location
Austin, TX
Any rise? I did 350' in 2" PVC largely because at that size there was zero impact on PSI at my GPM rate. I know PVC has doubled or more in cost... It's worked fine so far, even in a really rocky soil about 24" down.
 
Last edited:
OP
B

bluedog225

Well-known member
Joined
Jan 31, 2012
Messages
3,391
Location
Texas
I need to go find the pressure at the road. All the calculations seem to start there. Or just guess at 1’ or 1 1/4 and hope for the best.
 