Look at my service disconect is it right???

cyamaha2007

Well-known member
Joined
Apr 20, 2009
Messages
2,001
Location
St.Charles MO
I went to tech school for electric trades but this seems odd to me. The utility company says my 320 amp meter base will power 2 200 amp panels. So i have a 320 amp meter that feeds a 200 amp disconect that then feeds a 100 amp shop service and a 200 amp house service. So am i pulling too much through my service disconect. The way i see it i only have 200 amps of available power for the house and shop when i should have 300 amps.

Now heres the curve ball. I want to redo the shop service and make it a 200 amp also. Will my meter have a 2 sets of lugs so i can feed 2 service disconects. I will be replacing the 2/0 wire to the shop and the panel in the shop. Please help me.
So in the end i want to keep the 200 amp disconect for the house. And then add another seperate 200 amp service disconect for the shop.
Thanks Chuck
 

Attachments

  • wire.jpg
    wire.jpg
    95.6 KB · Views: 123
To avoid these ads, REGISTER NOW!

Alchymist

Well-known member
Joined
Mar 1, 2009
Messages
4,423
Location
Central PA
I'd chat with the POCO- they will know if the meter can be double lugged. You'll have to contact them anyway to have the meter pulled to rewire the service. Might touch base with your local inspector also.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Looks like a plan to me...

I'd chat with the POCO- they will know if the meter can be double lugged. You'll have to contact them anyway to have the meter pulled to rewire the service. Might touch base with your local inspector also.

320 meterbases usually come with teardrop lugs made for 2 wires.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
in the existing situation, what protects the 100 amp feeder?

the way you want to do it is how it should be. Pull a permit, coordinate with poco, and you should be good to go.
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,926
Location
oregon
Your second drawing is similar to what I have. I have a Square D CU12L400cb meter base/box. It came with one 200A breaker installed. It has a slot for a second 200A built in. So the box does what you need. In addition it has 8 slots for other breakers (qd?) that I use for outside power and the well house. I think there might be a picture of it in my build thread below. Also at
http://ecatalog.squared.com/pubs/El...ation Service Entrance Devices/4119HO0401.pdf

One other snag I ran into was the POCO wanting to know exactly what I was going to run that required 200A to the shop. I think that they were trying to size the feed wires and make sure that they had enough transformer.

lg
no neat sig line
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
C

cyamaha2007

Well-known member
Joined
Apr 20, 2009
Messages
2,001
Location
St.Charles MO
I dont have building permits to pull. Its no mans land out here. There is a 100 amp breaker inside of the service disconect that is there now. The disconect has spots for more breakers but if i do that i will still be pulling more than 200 amps through my 200 amp disconect unless its ment for that. I dont understand why they would even put a spot for breakers when anything you add will over do it.
 

jkeyser14

Well-known member
Joined
Dec 19, 2008
Messages
1,823
Location
(rural) Maryland
Just so you know, 2/0 won't cut it for 200 amps. You need 3/0 copper or 4/0 aluminum for a true 200 amp feed (or larger if it's a long run and voltage drop is an issue).
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
I dont have building permits to pull. Its no mans land out here. There is a 100 amp breaker inside of the service disconect that is there now. The disconect has spots for more breakers but if i do that i will still be pulling more than 200 amps through my 200 amp disconect unless its ment for that. I dont understand why they would even put a spot for breakers when anything you add will over do it.

does that 'disconnect' have a main breaker? Sounds like a feedthrough panel. Pretty common, has input from the meter, main breaker, feedthrough lugs that go to the house subpanel, and 4 or 8 breaker spaces for smaller feeders to shop, outdoor lights and receptacles, pool, etc.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I dont have building permits to pull. Its no mans land out here. There is a 100 amp breaker inside of the service disconect that is there now. The disconect has spots for more breakers but if i do that i will still be pulling more than 200 amps through my 200 amp disconect unless its ment for that. I dont understand why they would even put a spot for breakers when anything you add will over do it.
Just because you got the big breakers doesnt mean everything you own and then some will be on at once. Lots of 200A panels have 600A of breakers installed.
 