does anyone know the color code (per nec) for a 400v 50 hz system
and also where in the code it talks about color cade tapeing wire.
thanks
 
To avoid these ads, REGISTER NOW!
OP
R

rkevins

Well-known member
Joined
Aug 6, 2011
Messages
955
Location
Central Arkansas
thanks nehog that likn does look like it will help..on the 50 hz yea I should have woke up more before I ask ( been up sense 3am) we are buildind equipment going overseas and having slow response to some questions
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,785
400V is not a US voltage, other then where white, green, & orange is used the NEC is silent on most color coding issues,BTW.
 

dave67fd

Well-known member
Joined
Apr 25, 2011
Messages
872
Location
Southern NH
Your requirements would probably be listed under the CENELEC standard. Also will depend on your phase requirements.
The wire should also be CE/VDE rated.
Most european countries have not harmonized their colour coding so variations can exist here as well.

L1 - Brown, L2 - Black, L3 - Grey, Ground-Green/Yellow

For cables with earth conductor the code is:
5 - conductor Green/Yellow, Blue, Brown, Black, Grey
4 - conductor Green/Yellow, Brown, Black, Grey
3 - conductor Green/Yellow, Blue, Brown

For cables without earth conductor it is:
5 - conductor Blue, Brown, Black, Grey, Black
4 - conductor Blue, Brown, Black, Grey
3 - conductor Brown, Black, Grey
2 - conductor Blue, Brown

My company purchases most of it's european wire from Lapp/Olflex or Hellucable.
 
Last edited:

MBfreak

MEMBER EMERITUS
Joined
Dec 10, 2010
Messages
2,301
Location
Linkoping , Sweden
A small update on parts of the answer from dave 67d

3phase 400 V 50Hz ( in reality Um =<1000V AC, same goes for 690 V plant)in Europe is in all modern installs done as a 5 wire system.
3 phase conductors, colors as stated
1 neutral conductor , labelled N, ALWAYS BLUE
1 protective earth, labelled PE, always yellow/green

3phase loads are connected between phases, some two phase loads exists and are connected between 2 phases. Single phase loads are connected phase to N at 230 V.

For objects that are just connected between phases, the N conductor need not be installed. ( Typical example a cable to a Y connected motor has L1,L2,L3 and PE)

For the first supply from a feeding transformer L1, L2 , L3 , PEN.
The PEN is a combined PE and N conductor, yellow/green rated for full thermal load . When it comes to the first fuse(MCB box) the PEN conductor goes to the PE common bar and from there a blue conductor goes either to the common N bar or to the N incoming terminal of the incoming RCB for the install.

All trades have their accepted terms and in Europe the term for the protective connection to earth is mostly earth wire. And the dictated abbreviation is PE ( for Protective Earth)

CENELEC is your friend, but one suggestion is to require that your customer seds you the latest update, so that you are sure to meet his terms .

Ola
 