Well-known member
Son called me while I was away today all in a panic. The stove and air conditioner were clicking loudly and some of the lights were going crazy. I instructed him to turn off the main breaker until I arrived.
I was expecting one of the main breakers were bad but it turned out that I only had 31 volts on one of the hot legs coming out the meter. POCO showed up and re-did all the connectors on the pole and stated that there was 120 coming out the transformer on both hot legs. He then pulled the meter and determined that sure enough, only had 30 or so volts at the meter.
He then concluded that it was an issue with the buried lines and called out the underground crew. He said they would probably not pull a new line but would install a special meter that would turn the 120 into 240. I scratched my head and nodded ok. I left home for a while and sure enough, when I returned, that is what they did. Looks like they ran the one good hot leg through some sort of transformer that evidently is able to generate an out of phase 120 leg.
I would imagine that I would be limited on current draw but no note was left. What I don't understand is how in the hell there could be a problem with this leg. I am not sure what gauge wire it is but it looks like about a 1/2" or 3/4" rope of copper. If this is one continuous wire from the meter to the breaker on the pole, how could the line be bad?
I was expecting one of the main breakers were bad but it turned out that I only had 31 volts on one of the hot legs coming out the meter. POCO showed up and re-did all the connectors on the pole and stated that there was 120 coming out the transformer on both hot legs. He then pulled the meter and determined that sure enough, only had 30 or so volts at the meter.
He then concluded that it was an issue with the buried lines and called out the underground crew. He said they would probably not pull a new line but would install a special meter that would turn the 120 into 240. I scratched my head and nodded ok. I left home for a while and sure enough, when I returned, that is what they did. Looks like they ran the one good hot leg through some sort of transformer that evidently is able to generate an out of phase 120 leg.
I would imagine that I would be limited on current draw but no note was left. What I don't understand is how in the hell there could be a problem with this leg. I am not sure what gauge wire it is but it looks like about a 1/2" or 3/4" rope of copper. If this is one continuous wire from the meter to the breaker on the pole, how could the line be bad?