It doesn’t really matter , this was for temporarily testing an electric motor.OSHA not approved because there is no ground wire.
Also, the black wire shouldn’t be in the neutral slot.![]()
are you referring to the transformer cutouts on the primary side? those wouldnt be anywhere close to 100a and they surely wouldnt trip with a welder load... theyre sized at primary voltage so the amp rating is much lower than you would think...I knew a farmer who ran his stick welder like that after the plug had got hot and melted (might have been a clue they were pushing it in the first place)
Problem was the workshop supply had been tagged directly into the Henley blocks coming off the meter, and it didn't have a distribution board, or fuses or anything.
The only overload protection was the main 100A supply fuse in the utility cutout ahead of the meter.
are you referring to the transformer cutouts on the primary side? those wouldnt be anywhere close to 100a and they surely wouldnt trip with a welder load... theyre sized at primary voltage so the amp rating is much lower than you would think...
No.are you referring to the transformer cutouts on the primary side? those wouldnt be anywhere close to 100a and they surely wouldnt trip with a welder load... theyre sized at primary voltage so the amp rating is much lower than you would think...
Awww okNo.
Secondly side.
UK domestic (also smaller 3 phase supplies).
The power comes in on a concentric cable, inner is about an 1/8" solid aluminium wire for the live, outer is several cores of copper for the neutral.
The "cutout" is where they make off this wire and join it into the meter (they don't have separate meter bases so connections have to be directly made)
The cutout has a fuse holder which can be a 60A to 100A fuse depending on the supply on the live, the neutral has the grounding connection joined in as well.
Henley blocks are large plastic cased brass terminal blocks that allow you to join up to 4 25mm square wires, the stuff we use from the meter to the distribution board, you need them when you are splitting your power to more than one main board.
So the farmer had fed their workshop (which only had a couple lights and a half dozen 13amp sockets for power) just by tagging a single cable in to an open spot in the Henley blocks.
If they had a short it would have tried to pull 100A at 230V which would have been interesting, there obviously was no RCD protection of any type.
In the UK on most supplies getting the utility to pull the main fuse is the only way to disconnect the supply (newer installations have an isolator switch that allows the user to disconnect)Awww ok
Here in the US there is no protection on the secondary side between transformer and meter