So eventually, I'm going to have to figure this out:
I got called to "help" a neighbor during the last "It's about to freeze". They have a well house. The complain was that the GFCI "outlet" wasn't working and they couldn't run a heater on the pump house... They were on "electrician" #3 and up against the freeze.
I went out there, sitting along side were 2-3 "old GFCI" outlets that had been replaced. I tested the existing one, it was fine. No problems. Traced everything internally on the pump house. Everything connected right, wired right, proper breaker size. No faults.
Only "code" fault I can see is that the "out building" does not have it's own ground. But it's on a 4-wire feed. No GFCI fault.
So I probed L1/N and L2/N.
L1/N was 109V.
L2/N was 141V.
L1/L2 ~240V.
Ballistically I determined that their little electric heater did not like 141V. It would not turn on.
I have not probed the main on the house... But they worked around by running an extension from the house, so I assume that's OK.. I could also "swap" the legs and run this on the 109V leg.
Any guesses on it if it's not the main?


I got called to "help" a neighbor during the last "It's about to freeze". They have a well house. The complain was that the GFCI "outlet" wasn't working and they couldn't run a heater on the pump house... They were on "electrician" #3 and up against the freeze.
I went out there, sitting along side were 2-3 "old GFCI" outlets that had been replaced. I tested the existing one, it was fine. No problems. Traced everything internally on the pump house. Everything connected right, wired right, proper breaker size. No faults.
Only "code" fault I can see is that the "out building" does not have it's own ground. But it's on a 4-wire feed. No GFCI fault.
So I probed L1/N and L2/N.
L1/N was 109V.
L2/N was 141V.
L1/L2 ~240V.
Ballistically I determined that their little electric heater did not like 141V. It would not turn on.
I have not probed the main on the house... But they worked around by running an extension from the house, so I assume that's OK.. I could also "swap" the legs and run this on the 109V leg.
Any guesses on it if it's not the main?