OK, I jumped the R and W1 and it powers the vent, short 3' run horizontal out side wall but no noise from igniter. The LED flashes Green fast,
manual indicates:
Control Status - Green LED Codes
Steady ON .......Normal Operation, No call for heat
Fast Flash ........Normal Operation, Call for heat
1 Flash .............System Lockout, Failed to detect or sustain flame
2 Flashes .........Pressure Switch Did Not Close within 30 Seconds of Venter
motor
3 Flashes .........High Limit or Flame Rollout Switch Open
4 Flashes .........Pressure switch is closed before venter motor is energized
Steady OFF .....Blown Fuse, No Power, or Defective Board
Flame Status - Yellow LED Code
1) Call for Heat - The thermostat calls for heat by energizing the “W” terminal. The control checks to see that the limit switch is closed and the pressure switch is open. If the limit switch is open, the control responds as defined in the “Abnormal Heat Cycle, Limit Switch Operation”. If the pressure switch is closed, the control will do four flashes on the green LED and wait indefinitely for the pressure switch to open. If the pressure switch is open, the control proceeds to prepurge.
The code doesen't suggest pressure switch? Thanks