3 Regulators. 1 at the tank, 1 at the house, and the genny has it's own separate regulator
I think you have a plugged line, maybe from a mud dauber. They can absolutely plug a line that line pressure won't blow out. Also your lines sound small for a Generac. Did you check the manual for recommended size?
http://skipd.artin.org/Pipe sizing for fuel gas.jpg
You have a regulator (#1) off the tank, a regulator (#2) at the generator, and a regulator (#3) at the house. #1 steps down your tank pressure to a supply line pressure, to feed the other 2 lines, which then steps down your pressure to their respective appliences (Generator or House). The Generator has a safety valve - if your pressure is too high or too low feeding it (say, you remove the regulator at the generator and try to feed it from the supply line pressure), it won't allow gas to flow. You're talking the difference between 5-10 PSI and 0.2 to 0.3 PSI (5-10 column inches)...
OR... If you're underpressure (the tank is too low or empty) it will seat this valve, and it may be stuck from years of non-use and an empty tank...
Then you have the control circuitry - the ECU - for the machine. Ours (a 22 KW Generac) will "no-start" under various fault conditions. I know ours had a recall of the control circuit board, they didn't advertise it but a number of them failed... The board controls almost all aspects of the unit...
You can get a PDF of the manual for the unit online (I have both the Operators and Service manual for ours) and I would recommend doing that so you know what the foibles of YOUR generator are...
They're otherwise pretty simple systems. Look up the installation instructions for YOUR unit, make sure it's set up for your generator, then start the troubleshooting process...