To avoid these ads, REGISTER NOW!

LVL bearing points

gregs

Well-known member
Joined
Mar 16, 2007
Messages
1,646
While looking at span tables for LVL's it also gives you the bearing point for the support at each end. So lets say I want to remove a wall between two rooms that are both 12' wide. But I only want the opening to be 10' leaving 12" on either side to serve as a visual separation of the rooms. The tables spec a minimum 3" bearing on each end. So you could use a beam that is 10' 6" long and incorporate the 3" of bearing surface into each 12" wall. What if I installed a 12' beam and 12" of bearing surface at each end to reduce the opening to 10'. Other than the extra expense of the longer beam and additional jack studs is there any problem doing this? I figure its not changing the weight carrying capacity of the beam as its still a 10' span. Would it just place the load over a larger area on the floor?
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,751
Location
Long Island
The bearing surface is the MINIMUM surface allowed by the LVL for that span. Less than that, and you will crush wood fibers of the LVL. More is fine, and may even be required depending on what the LVL is sitting on. If you're supporting it with wood for example, that wood column may require a larger bearing area than the LVL.
 
OP
G

gregs

Well-known member
Joined
Mar 16, 2007
Messages
1,646
Understand. I was thinking of it only from a load bearing point on the floor. So in theory increasing the area like I am thinking about could be a positive thing. Thanks
 

juddspaintballs

Well-known member
Joined
Sep 1, 2011
Messages
324
Location
Hedgesville, WV
You typically buy LVLs by the foot or two foot increments, so you're buying 11' or 12' of LVL either way. It would be silly to cut 6" or 18" off of the LVL to get to the minimum bearing distance, especially since you can fit a 12' LVL in the space.


Are you doing 2x4 or 2x6 walls? Either way, you're likely going to need at least a pair of studs nailed together at the end of those walls to bear the beam load.
 

Hank11

Well-known member
Joined
Aug 19, 2019
Messages
1,169
Location
Tennessee
Whats holding up the floor and particularly the area under your 12” walls that support the beam? This can be important.
 
OP
G

gregs

Well-known member
Joined
Mar 16, 2007
Messages
1,646
It is a 2x4 wall. I understand that 2-2x4 jack studs is the minimum at each end. My plan would be to buy a 12' beam and fill the 12" in each end to create the 10' opening. So for it to meet its 10' span rating the jack studs need to be at the edge of the 10' opening. So would it be a waste to just make the entire 12" out of studs? And would you have them sitting directly on the floor or on a 12" bottom plate? Its on a reinforced concrete floor footing.
 

Hank11

Well-known member
Joined
Aug 19, 2019
Messages
1,169
Location
Tennessee
So there is a concrete footing under the full 12” of the little walls?
If so, you are good to go.
 
OP
G

gregs

Well-known member
Joined
Mar 16, 2007
Messages
1,646
According to the foundation plan there is a footer / beam running under the wall area. The foundation plan shows a grid like layout of these footer / beams that are throughout the slab.
 
To avoid these ads, REGISTER NOW!

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,996
Location
Thousand Islands NYS
If this is all on a slab? If so, each 12" wall could be 12" top and bottom plates, and 2 studs. Another stud or two is fine if it makes building it simpler.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,751
Location
Long Island
If this is all on a slab? If so, each 12" wall could be 12" top and bottom plates, and 2 studs. Another stud or two is fine if it makes building it simpler.
Close, but no. That would give insufficient bearing surface as discussed above. Three studs per 12" wall, with a pair at the end of the span might satisfy the bearing surface, but you still need a king stud to go with those two jack studs, so you're looking at 4 studs per 12" wall. And that's assuming the pair of jack studs can carry the compressive load that the removed wall would have carried before. I'm not sure a pair could, but with the third king stud involved, I'm betting it will be fine.
 
Last edited:

CraigStu

Well-known member
Joined
May 22, 2014
Messages
4,084
Location
Blacksburg, Va
You need a bottom plate and, on concrete, it may need to be pressure treated. I like your plan of supporting a full 12" of the lvl on each end.
 
OP
G

gregs

Well-known member
Joined
Mar 16, 2007
Messages
1,646
Would a bottom or top plate cause an issue regarding the compressive load for the jacks? Thinking end grain vs face grain? Plan would be to leave the top plate in place as it would serve as a tie plate to the joists as its nailed into them already. Double or triple king studs wouldnt be an issue as it would only be shortening the beam slightly. By the time you do multiple kings and jacks in a 12" space I think I might as well make it solid 2x4's as there isnt much to save.
 

Hank11

Well-known member
Joined
Aug 19, 2019
Messages
1,169
Location
Tennessee
The bottom plate compression will be so little you will never notice it. It would be very hard to fasten the studs to the concrete without a bottom plate and you'd have nothing to nail your finish wall to at the bottom.
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,996
Location
Thousand Islands NYS
Close, but no. That would give insufficient bearing surface as discussed above. Three studs per 12" wall, with a pair at the end of the span might satisfy the bearing surface, but you still need a king stud to go with those two jack studs, so you're looking at 4 studs per 12" wall. And that's assuming the pair of jack studs can carry the compressive load that the removed wall would have carried before. I'm not sure a pair could, but with the third king stud involved, I'm betting it will be fine.
3" is 2 studs. Doesn't matter if nailed together or a foot apart - it's still 3" of bearing. Wether you need a king or not depends on what it's butting into and what it's being sheathed with.
 

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
2,005
Location
East Cobb County, Georgia
3" is 2 studs. Doesn't matter if nailed together or a foot apart - it's still 3" of bearing. Wether you need a king or not depends on what it's butting into and what it's being sheathed with.
Strictly from the point of view of bearing this is true, however Herr Euler reminds us that nailing the 2 together will make for a much stiffer post.
 

Beamer

Well-known member
Joined
Jun 21, 2020
Messages
1,461
Location
Northeast
A thought. The information that you noted about a (minimum) 3" of bearing on supports, I would assume that it was in regards to the bearing stresses, but there is another thing that needs consideration. Your actual loads being transferred to the studs and the stud heights will have an impact on determining if (only) 2 studs will be adequate acting as posts. This is a different topic than how much bearing is required. That is a calculation item and not a rule of thumb or reference table solution.
 
To avoid these ads, REGISTER NOW!
Top Bottom