Mag starter help

terryo1965

Well-known member
Joined
Nov 22, 2011
Messages
75
Location
Ann Arbor, Michigan
I have an old IR T30 2 stage compressor that was converted to a 3HP 1ph motor before I got it. It was originally a 5hp 1ph unit. My problem is as the pressure starts building there was a "banging" noise out of the starter box. I took the cover off and I can see the magnetic button going in and out creating this popping noise. I was told it could be low voltage to the starter causing the coil to not "hold" and I need more robust wiring to the starter.

The wiring from the starter to the wall plug is 12 gauge and the plug end is a 20amp 220v. I am running a 20amp breaker. I thought this might be the problem but I was reading the starter information that came with the unit and it spec's out 12 gauge wiring to the starter.

Do you think the wiring to the starter should be 10 gauge? Is the 20amp breaker too small?

I have been running the compressor for a couple years with this setup and it has worked okay. The popping started right before the pressure switch would turn off the compressor off but after several months it is popping at lower and lower pressures.

Any input would be appreciated!
Thanks,
Terry
 
To avoid these ads, REGISTER NOW!

Zrexxer

Well-known member
Joined
Jan 23, 2007
Messages
5,058
Location
Pflugerville, TX
Could you have a 220V coil that's only being fed from one leg? Some coils are 120V and it may have been wired wrong.
 
OP
T

terryo1965

Well-known member
Joined
Nov 22, 2011
Messages
75
Location
Ann Arbor, Michigan
I think the starter was wired correctly. I was a used unit that came out of an Detroit Edison service center so I would hope they know what they are doing!! Plus the thing has worked okay for a couple years, although it doesn't get a lot of use.
 
To avoid these ads, REGISTER NOW!

71flh

Banned
Joined
Jun 15, 2011
Messages
379
Maybe you could look at the thing and see what the ratings are.
Maybe measure the voltage with and w/o a load, and across the coil when running.
 

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
It sounds to me like your pressure switch is malfunctioning and cycling the mag switch until the compressor stops.
 

Fred43

Member
Joined
Apr 20, 2012
Messages
14
Location
Bellingham, MA
The presure switch is the easiest point to check for pitted contacts, dirt, loose connections. If this does not solve the problem check the stater for the same types of problems. Check for loose wires !!!
 