Magnetic starters

bronc3buster842001

Well-known member
Joined
Dec 1, 2009
Messages
232
Location
Somewhere in Missouri
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,763
they only get more expensive. that looks to be a no name product.

No name ChiCom junk, doubt it is UL or any other NRTL listed. The OP would be better off w/ NEMA style starter made by Siemens (formerly Furnas), Allen-Bradley, or Square D.
 
To avoid these ads, REGISTER NOW!

ffast65

Well-known member
Joined
Mar 8, 2014
Messages
159
Location
Columbia Station, OHIO
resurrecting this old thread, Bought an champion with a Siemans 16BF35BGASY starter that was used on a 7.5 HP 3 Ph motor that pulled 21.7 amps at 208.

Going to buy a L1510T which will pull 31 amps. Can this same motor started be used? The siemans site says its rated for 30 amps at 203/240 v.

If not, can it be converted?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,763
resurrecting this old thread, Bought an champion with a Siemans 16BF35BGASY starter that was used on a 7.5 HP 3 Ph motor that pulled 21.7 amps at 208.

Going to buy a L1510T which will pull 31 amps. Can this same motor started be used? The siemans site says its rated for 30 amps at 203/240 v.

If not, can it be converted?


Simple answer, no. A single phase motor will require a larger starter then the same size 3Ø motor & needs to be rated for that motor.
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
resurrecting this old thread, Bought an champion with a Siemans 16BF35BGASY starter that was used on a 7.5 HP 3 Ph motor that pulled 21.7 amps at 208.

Going to buy a L1510T which will pull 31 amps. Can this same motor started be used? The siemans site says its rated for 30 amps at 203/240 v.

If not, can it be converted?

Simple answer, no. A single phase motor will require a larger starter then the same size 3Ø motor & needs to be rated for that motor.

Norcal is correct. It's a common mistake a lot of guys make. I was doing a job recently where we were using an electrical contractor to do an install on 3 large systems...3ph motors from 5 HP up to 325 HP. Part of the install included installing local disconnects. They looked at the motor FLA and bought disconnects based on the rating.....they were not happy when I pointed out to them that they had to look at the HP rating for a given voltage...."See, right there on the label inside the door". They had to replace half of them.

I was a bit surprised to find to electricians with 20+ years experience each and they didn't know that little fact.
 

ffast65

Well-known member
Joined
Mar 8, 2014
Messages
159
Location
Columbia Station, OHIO
NorCal and John

Thanks for the replies. As I haven't pulled the trigger on the motor, I could use some sizing advise.

Will this existing one cover a 5 hp 1phase 1740 motor?

If I used a 7.5 hp, do I need to jump to a 40 amp unit?
This is an area I don't have any work experience with motor starters. I'm assuming my existing can't be upgraded
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,030
Location
Modesto, CA
NorCal and John

Thanks for the replies. As I haven't pulled the trigger on the motor, I could use some sizing advise.

Will this existing one cover a 5 hp 1phase 1740 motor?

If I used a 7.5 hp, do I need to jump to a 40 amp unit?
This is an area I don't have any work experience with motor starters. I'm assuming my existing can't be upgraded

Motor starters are mainly rated and sized based on HP NOT amps! This is because motors have in-rush starting currents! The in-rush current of a motor can be 3x-6x the FLA!!!
 