ran sub panel to my detached garage using 2224 mobile home feeder. looking at the pictured, my grounds are each grounded to the boxes. i was told that was ok but not preferred. should i move each respective ground to the bus bar as i circled in the pictures?

the sub panel has the ground bars bonded to the panel, neutral bars are not. also have two copper rods going to one of the sub panel ground bus bar.
 

Attachments

  • 93FE91A3-80EB-4B11-96EB-4782EBDA82AC.jpg
    93FE91A3-80EB-4B11-96EB-4782EBDA82AC.jpg
    114.2 KB · Views: 120
  • 1296F409-9D06-476C-A4D4-6DBA1E422261.jpg
    1296F409-9D06-476C-A4D4-6DBA1E422261.jpg
    83.8 KB · Views: 125
To avoid these ads, REGISTER NOW!

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
#2 AL only good for 90 amps since not feeding an entire dwelling.
Grounds are be fine as box to box. Getting #4 into those bus bars would most likely require an adapter.
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
M

mopar4u

Well-known member
Joined
Nov 25, 2012
Messages
131
#2 AL only good for 90 amps since not feeding an entire dwelling.
Grounds are be fine as box to box. Getting #4 into those bus bars would most likely require an adapter.

yeah i know i need a 90 amp breaker instead of the 100. store didnt have a 90 at the time. highly doubt ill ever come close to 90/100 usage but eventually ill get a 90
 