main breaker on 100amp sub panel, do i need it?
Stevenanto
Montreal Canada
Hi everyone,
I have yet another electrical question. I have bought the subpanel in the link below. I passed a wire from my 200 amp main panel to this new subpanel. I have two different people telling me two different things. One of them says that i dont have to put the 100amp main breaker on the sub panel because i have a 100 amp breaker coming from my main. The second person says I have to put yet another breaker in my subpanel at the top.
which on is right? would it work either way, i dont want it to catch fire. I called the company schneider but they can give me an answer until Monday.
here is a link of the exact panel that i bought.
https://www.rona.ca/en/panel---electrical-panel-0265030--1
thanks in advance
pattenp
Virginia - USA
If the subpanel is installed in the same structure as the main panel then the main breaker is not needed in the subpanel. If the subpanel is installed in a detached structure from where the main panel is installed then a main breaker is needed in the subpanel. At least that's how it is in the US.
Hi everyone,
thanks in advance
Is the subpanel in an attached or detached structure?
What kind and size of wire did you use?
Aceman
Eastern Oregon
Just a little correction to this.
A separate structure needs a means to disconnect the wiring entering the structure. A main breaker is one option. So is a disconnect switch.
As mentioned above you can also use the 6 disconnect rule rather than one main breaker.
225.39(D) requires a 60 amp rating minimum or combination of, to meet the 60 amp rating.
Low277
Minnesota
Rules vary between US and Canada, also rules can vary by areas within the same state. In many instances the Authority Having Jurisdiction can interpret things differently.
Many years ago I had a local inspector that would require a sub panel in same structure have a main breaker if the sub panel had any single pole breakers in it. I forget what his reasoning for it was.
sberry
Brethren, Michigan
I don't think it's drastically different. While it may be accurate thay ahi may read it different most of this isn't different state to state,, some minor exceptions. Local amendments are really very few and most originate from ,,,,,,,, "someone told me",, and another from,,, "I was always told".
MattT
From an engineering standpoint you don't need a main breaker in the sub panel. The 100A breaker in the main panel will provide overcurrent protection.
If you are forced, or want, to comply with local codes a disconnect may be required and using a main breaker in the sub could be the easiest way to comply with that requirement.
The Cobbler
if the sub panel is in a detached building, it needs a disconnect. the 100 amp breaker can be used as a disconnect. even if the service to the sub is less than 100 amps.
not sure about the code if panel is in same structure
mike93lx
Richmond, VA
thanks everyone for the help! very informative as always. I will end up getting the breaker. better safe than sorry
for the $40 a 100a breaker costs, I'd put one in too. A lot easier to do it up front than add it later and it's nice to be able to easily shut down a panel for work.
Falcon67
Merkel, TX
Without regard to codes, I find it good to have a main in a big sub panel - it's handy to be able to shut down the whole panel if needed.
sberry
Brethren, Michigan
That s part of the reasoning behind no main in some of the subs, it actually does shut the whole panel down when you turn off the feed breaker.
Because 1 doesn't shut the power off to that panel. There are live lugs above the main.
That really depends on the panel and how its made
many panels have the feeder ungrounded conductors going straight to the main so there is no live lugs with the breaker off other than the ones on the line side of the breaker.
mike93lx
Richmond, VA
i dunno, of all the times I've killed a main to work in a panel, the lugs at the top weren't my concern, it was the buss bars and breaker connections around where I was working. sure an extra measure of safety isn't bad, but is it really needed?
There is always power upstream at some point, whether at another panel, the lugs, meter socket, pole...
Stevenanto
Montreal Canada
the cost of this one is about 90-100$ in my area, everything is much cheaper in the US lol. thats not the point, I will be putting it in regardless of the cost, better safe than sorry.
sberry
Brethren, Michigan
The code writers do not care what "your concern" is. They do this from decades of forensics, they have a good reason for what they do and the way it is.