Main breaker tripped but one circuit stayed on

To avoid these ads, REGISTER NOW!

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
So this is weird. We had an ice storm yesterday and during a brownout the main breaker in my garage tripped. This garage is on its own meter.

One of the circuits ended up remaining on. I know this because it is the circuit that powers a surveillance camera and fiber optic feed from my house and I can see the footage before and after the brownout.

So something is seriously mis-wired in my panel right? What could even cause this? All other circuits in the garage--other outlets, garage opener, etc were off, but this one circuit remained on with the main breaker in the 'tripped' position.
Battery backup?
 

ipgenie

Well-known member
Joined
Jan 29, 2020
Messages
562
Location
Idaho
The meter/load combo that was installed on my shop in 2001 had a meter socket, a 200a main with maybe 6 breaker slots and feed through lugs going to the house. It also had another two pole spot above the 200a main that was fed separately from the meter and not protected by the the 200a main. This breaker was used to power my well pump and remained on when the 200a main was off.

Maybe the OP has a similar combo panel with two main feeds from the meter, one 200a and another smaller. I don't know if that is a currently used panel though, lots of NEC changes since 2001. A picture would be helpful.

This pic is upside down but you can see the two separate feeds from the meter. I replaced the panel 5 years ago with a 380A in order to have additional bus capacity for the solar inverters. I don't know why I still have it laying around. Can't get rid of anything I guess.

Screenshot_20250107_025914_Gallery.jpg
 
Last edited:

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,268
Location
Penngrove, California
Are you certain it was a live camera image you saw after the brown out? I am not familiar with Ubiquiti cameras but with my camera system, if there is a connection loss, or power loss, it will retain the last captured image. Do you store images on any local device, cloud storage or on your phone?
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,924
Location
Austin, TX
Are you certain it was a live camera image you saw after the brown out? I am not familiar with Ubiquiti cameras but with my camera system, if there is a connection loss, or power loss, it will retain the last captured image. Do you store images on any local device, cloud storage or on your phone?
Ubiquiti will notify you when the camera goes offline. There is also a live feed function that it will default to.
 
OP
T

teknikfrog

Well-known member
Joined
Apr 29, 2023
Messages
216
The OP said it would be a couple days before they could get pics...
Yeah it's been freezing cold and we have ten inches of snow on the ground and my garage is a hike uphill from my house. Forgive me.

Here is a pic:

photo_2025-01-12_15-39-01.jpg

I've only been inside a handful of panels in my lifetime but everything here looks completely normal to me. Side note I love all the extra space in here.

BTW this garage is new construction, around five years old.

I did test turning off the main breaker and my cameras shut off.

So it looks to me like what happened is when the main breaker tripped it failed to trip fully and I'm guessing one leg stayed on which would explain why most items were out but the cameras remained on. They actually did drop out for 12 seconds or so (it keeps logs) but came back on and remained on for half a day or so until I noticed the main breaker trip and re-set it.

Question; how big of a deal is this? Do I need to explore the issue further or just let it go?
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,493
Location
VT
What makes you think the main was tripped in the first place?

What made you check it?
 
OP
T

teknikfrog

Well-known member
Joined
Apr 29, 2023
Messages
216
What makes you think the main was tripped in the first place?

What made you check it?
All my lights and garage door opener were out.

So I opened the panel and noticed the main breaker was in the 'tripped' position.
 

ipgenie

Well-known member
Joined
Jan 29, 2020
Messages
562
Location
Idaho
Looks like all 3 120v branch breakers are on the same side. If one is hot, all of them should be.
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,009
Location
Central Iowa
If the main didn't fully open (both poles), and the lower right cb had power, then so would the lower left cb.
Right, but he said the cameras didn't shut off when the main tripped. He also said in post #59 that the cameras are on the bottom right breaker. Thus, if the main didn't open fully and the cameras really were still on, whatever is fed from the bottom left breaker would have had to also be on.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,053
Location
NJ
Right, but he said the cameras didn't shut off when the main tripped. He also said in post #59 that the cameras are on the bottom right breaker. Thus, if the main didn't open fully and the cameras really were still on, whatever is fed from the bottom left breaker would have had to also be on.
Agree, but post 63 says it would NOT have been on.
 

Higgins

Well-known member
Joined
Dec 25, 2009
Messages
1,944
Location
Shepheardsville, KY
The camera IS poe but it gets its power from the garage.

The only way the house could be feeding power is via some very weird grounding ******* occurring via the armor on the buried fiber optic cable.. I do wonder if maybe that's the case. Should be easy to test for once this storm moves out.

I'll update the thread but it will be a couple days. I'll also snap a pick of my panel with the cover off.
Some security systems have an internal battery to provide battery power during disturbances….
 

Herzog

Member
Joined
Feb 6, 2019
Messages
16
Location
Star Valley, Wyoming
Pretty odd that your lights were out if one leg was still live, since all your 20 amp breakers are all on the same leg.
edit, nm. The top breaker is on the left leg.
 

MongoTA

Well-known member
Joined
Mar 10, 2018
Messages
1,017
Location
CT
So this is weird. We had an ice storm yesterday and during a brownout the main breaker in my garage tripped. This garage is on its own meter.

One of the circuits ended up remaining on. I know this because it is the circuit that powers a surveillance camera and fiber optic feed from my house and I can see the footage before and after the brownout.

So something is seriously mis-wired in my panel right? What could even cause this? All other circuits in the garage--other outlets, garage opener, etc were off, but this one circuit remained on with the main breaker in the 'tripped' position.
I can offer this. I have a SquareD 200A panel.

Quite a few years ago I turned off the main breaker in my new panel which should have killed power to the entire house and was about to dig in and add more circuits when I heard music coming from upstairs. I did not own a battery powered radio. Went upstairs and with the main breaker off, the outlets in that room were still powered. Went back to the panel and with a meter found that with the main breaker off one buss was powered, one was not powered. huh.

Contacted SquareD, the person I spoke with "knew of the problem". Didn't seem to happen often, but it was a mode of failure they knew did happen. They recommended changing out the panel as a whole, I bought a new panel, went outside and pulled the meter, popped the breakers off the busses and folded them back out of the way, then just swapped out the buss and main breaker assemblies between the new and old cabinets. Then snapped the breakers back on the new buss assembly. They sent me a check for a few hundred dollars.
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,268
Location
Penngrove, California
What is on the 240VAC feed on the upper left? Perchance did you try to use it during this "outage", as it would have only one side of 240 and should have been dead.
I can offer this. I have a SquareD 200A panel.

Quite a few years ago I turned off the main breaker in my new panel which should have killed power to the entire house and was about to dig in and add more circuits when I heard music coming from upstairs. I did not own a battery powered radio. Went upstairs and with the main breaker off, the outlets in that room were still powered. Went back to the panel and with a meter found that with the main breaker off one buss was powered, one was not powered. huh.

Contacted SquareD, the person I spoke with "knew of the problem". Didn't seem to happen often, but it was a mode of failure they knew did happen. They recommended changing out the panel as a whole, I bought a new panel, went outside and pulled the meter, popped the breakers off the busses and folded them back out of the way, then just swapped out the buss and main breaker assemblies between the new and old cabinets. Then snapped the breakers back on the new buss assembly. They sent me a check for a few hundred dollars.
That is interesting! I wonder if Square D ever issued some bulletin or advisory on the issue. They are no small player I am surprised those in the business have not ran into this, like some of the Federal Pacific or Zinsco issues.
 
OP
T

teknikfrog

Well-known member
Joined
Apr 29, 2023
Messages
216
What is on the 240VAC feed on the upper left? Perchance did you try to use it during this "outage", as it would have only one side of 240 and should have been dead.
Air compressor. Did not try to use it.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
I can offer this. I have a SquareD 200A panel.

Quite a few years ago I turned off the main breaker in my new panel which should have killed power to the entire house and was about to dig in and add more circuits when I heard music coming from upstairs. I did not own a battery powered radio. Went upstairs and with the main breaker off, the outlets in that room were still powered. Went back to the panel and with a meter found that with the main breaker off one buss was powered, one was not powered. huh.

Contacted SquareD, the person I spoke with "knew of the problem". Didn't seem to happen often, but it was a mode of failure they knew did happen. They recommended changing out the panel as a whole, I bought a new panel, went outside and pulled the meter, popped the breakers off the busses and folded them back out of the way, then just swapped out the buss and main breaker assemblies between the new and old cabinets. Then snapped the breakers back on the new buss assembly. They sent me a check for a few hundred dollars.
I remember hearing something about an issue with SQ D but dont recall what it was

which model line? homeline or QO?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,009
Location
Central Iowa
I remember hearing something about an issue with SQ D but dont recall what it was
If it's the one I'm thinking of, it had something to do with an improperly torqued neutral lug on the plug on neutral QO panels. I don't remember if Homeline was included or not.
which model line? homeline or QO?
Homeline and QO single phase have the same main breakers if that's what you are trying to figure out. That one is a QOM200.
 