TexasK5
Active member
Getting ready to connect the main electrical to a cabin that was just built that is next to an existing structure that already has power.
Originally, when the barn was built, running that line was part of the deal with the builder. What I didn't do was make sure that the line he was planning to run was large enough for future plans that we knew included a cabin. After the line was in, I found out it was 1/0 aluminum. This is "adequate" for the barn, but not enough to continue on to the new cabin.
For the cabin, the underground run will be ~250 feet, and then up to the panel on the pole and into the cabin.
Currently there is a feed through panel at the pole and the 1/0 is connected at the feed through lugs. I am planning to install a 125A double pole breaker, move the 1/0 barn feed to the new breaker and connect the cabin feed to the feed through lugs.
Based on voltage drop and the expected loads (standard cabin stuff, all electric, no gas), I believe that 4/0 aluminum will be enough for that distance. Of course, 3/0 copper would work as well, but is considerably more expensive.
Looking for advice on the most cost effective way to do this. I see some 4/0-4/0-4/0 aluminum wire available that indicates that it is suitable for direct burial. Is this a good idea? Would I just have conduit where it exits the ground at the pole and cabin and everything in between is in the ground, no conduit?
I haven't seen any 3/0 copper suitable for direct burial, so that means 250' of conduit as well. Then it looks like the conduit needs to be glued together first and then pull the cable. Seems like pulling that may be beyond a diy task. Is there an easier way to do this that I am missing?
A sketch is attached to show the layout.
Any help is appreciated.
Thanks
Originally, when the barn was built, running that line was part of the deal with the builder. What I didn't do was make sure that the line he was planning to run was large enough for future plans that we knew included a cabin. After the line was in, I found out it was 1/0 aluminum. This is "adequate" for the barn, but not enough to continue on to the new cabin.
For the cabin, the underground run will be ~250 feet, and then up to the panel on the pole and into the cabin.
Currently there is a feed through panel at the pole and the 1/0 is connected at the feed through lugs. I am planning to install a 125A double pole breaker, move the 1/0 barn feed to the new breaker and connect the cabin feed to the feed through lugs.
Based on voltage drop and the expected loads (standard cabin stuff, all electric, no gas), I believe that 4/0 aluminum will be enough for that distance. Of course, 3/0 copper would work as well, but is considerably more expensive.
Looking for advice on the most cost effective way to do this. I see some 4/0-4/0-4/0 aluminum wire available that indicates that it is suitable for direct burial. Is this a good idea? Would I just have conduit where it exits the ground at the pole and cabin and everything in between is in the ground, no conduit?
I haven't seen any 3/0 copper suitable for direct burial, so that means 250' of conduit as well. Then it looks like the conduit needs to be glued together first and then pull the cable. Seems like pulling that may be beyond a diy task. Is there an easier way to do this that I am missing?
A sketch is attached to show the layout.
Any help is appreciated.
Thanks