Trying to get power to a shed. Picked up a square d 70amp lug load center. Ran the conduit today and wired every thing up inside. Went to wire the service wire and think i made a mistake on choosing the wire. 8/2 is was i bought thinking i could run just 120 out to it on a 40amp breaker. Well the load centers power lugs are seperate, meaning i will have to have 2 hot wires powering each pole. Can i use the 8/2 for this? I would have to use the ground wire as the neutral to feed back to the meter box, and add a ground bar to the sub pannel and do a earth ground. Ideal would be a 10/3 wire or 8/3 but would hate to have to pull all the wire in the conduit.
 

Attachments

  • 20240203_151425.jpg
    20240203_151425.jpg
    363.7 KB · Views: 51
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,991
Location
Modesto, CA
Trying to get power to a shed. Picked up a square d 70amp lug load center. Ran the conduit today and wired every thing up inside. Went to wire the service wire and think i made a mistake on choosing the wire. 8/2 is was i bought thinking i could run just 120 out to it on a 40amp breaker. Well the load centers power lugs are seperate, meaning i will have to have 2 hot wires powering each pole. Can i use the 8/2 for this? I would have to use the ground wire as the neutral to feed back to the meter box, and add a ground bar to the sub pannel and do a earth ground. Ideal would be a 10/3 wire or 8/3 but would hate to have to pull all the wire in the conduit.
yeah lotta things wrong here.

by 8/2 i assume you got NM-b. this is not permitted underground

you need 4 conductors total.

no you cannot use the bare ground as a neutral.

grounding electrodes do not take the place of an EGC in a feeder. you need both.

you will unfortunately need to pull the wire out and start over

what size conduit did you run? I would use individual THWN conductors.

refer to post #3 and #4 in the Electrical FAQ sticky for guidance on how to do this

 
OP
C

caleb90

Well-known member
Joined
Apr 12, 2020
Messages
54
Location
at home
It was uf wire, 1 in conduit so it was tight. Will buy single 10g conductors and rerun every thing
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,374
Location
VT
yeah lotta things wrong here.

by 8/2 i assume you got NM-b. this is not permitted underground
They say it's UF so that seems fine
you need 4 conductors total.

no you cannot use the bare ground as a neutral.

grounding electrodes do not take the place of an EGC in a feeder. you need both.

Is there a correct way to run a 120v only sub panel?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,406
Location
Richmond, VA
It was uf wire, 1 in conduit so it was tight. Will buy single 10g conductors and rerun every thing
If you want 120v only, you are fine to keep it. Just need to feed from a single pole breaker and tie the two buss bars together in the sub.

If you want 240v or 2x40a 120v, you need to run 4 conductors

Did you put the whole run in conduit? The purpose of uf is to run it direct burial and only protect with conduit where subject to damage above ground. When running conduit end to end, Thwn or XHHW are the best wires to use
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,374
Location
VT
Yeah, 3 conductor, as the OP has. Just tie the two poles together in the subpanel and dont run any two pole breakers

I mean, I knew that, but I'm not an electrician ;) .

Should have said code compliant.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,374
Location
VT
I am not aware of any code issues with what I shared

Could also just light up one side of the subpanel
Well, if it was me and I wanted 120v only, I'd put that hot line to a blue wirenut along with 2 other pieces, 1 to each hot lug.

Neutral to neutral, bare ground to ground.

But, I would have planned ahead and done a 240v sub if I was doing all that work.
 
To avoid these ads, REGISTER NOW!

Tundra1

Well-known member
Joined
Sep 3, 2023
Messages
196
No matter if it was inspected or not it ought to be correct.
Hahaha! I wasn't implying OP should cut corners or do something wonky. 100% agree it needs to be correct. Partly it was idle curiosity and partly figured the responses may be more specific for working towards an inspection. Mostly idle curiosity....
 

BreeStephany

ALLIANCE MEMBER
Joined
May 19, 2012
Messages
849
Location
Oregon
Is it going to be inspected?
It doesn't matter whether or not it is inspected or not, it should be done correctly and to code. Code exists to ensure that things are properly and safely installed and to ensure that there are not issues down the road due to the installation methods used.
 
OP
C

caleb90

Well-known member
Joined
Apr 12, 2020
Messages
54
Location
at home
Well its all done. Decided that i didnt need 240 out there. Only have one 15amp circuit for lights and two 20amp circuits with 4 outlets on each circuit. Popped the trip bar off the double pole breaker, used one side for my 120v hot. Used a jumper in the sub pannel to make both lugs hot. I used direct burrial wire in the pvc conduit as a percaution. I dont see why that would be agaisnt code
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,406
Location
Richmond, VA
Well its all done. Decided that i didnt need 240 out there. Only have one 15amp circuit for lights and two 20amp circuits with 4 outlets on each circuit. Popped the trip bar off the double pole breaker, used one side for my 120v hot. Used a jumper in the sub pannel to make both lugs hot. I used direct burrial wire in the pvc conduit as a percaution. I dont see why that would be agaisnt code
It isn't against code. It's just a pain in the *** and gives no benefit over conduit and thwn wire.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,374
Location
VT
Well its all done. Decided that i didnt need 240 out there. Only have one 15amp circuit for lights and two 20amp circuits with 4 outlets on each circuit. Popped the trip bar off the double pole breaker, used one side for my 120v hot. Used a jumper in the sub pannel to make both lugs hot. I used direct burrial wire in the pvc conduit as a percaution. I dont see why that would be agaisnt code

Not sure what you mean by that....

But if you've backed through a breaker it needs a hold down kit.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,253
Location
Coastal NJ
Was going to use a double pole 30amp in the meter box.

Well its all done. Decided that i didnt need 240 out there. Only have one 15amp circuit for lights and two 20amp circuits with 4 outlets on each circuit. Popped the trip bar off the double pole breaker, used one side for my 120v hot. Used a jumper in the sub pannel to make both lugs hot. I used direct burrial wire in the pvc conduit as a percaution. I dont see why that would be agaisnt code

If I understand this correctly, you have an unused pole on the 30A breaker in the meter box. That is fine. The "trip bar" is actually a handle tie. And depending on the brand, some breakers have an internal common trip and some rely on the handle tie to perform that function.

Since you are only using 1 pole of the 2 pole breaker, all that common trip and handle tie function is irrelevant.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,967
Location
Central Iowa
That isn't a trip bar, it's a handle tie so that both sides are turned on and off together. The common trip is internal, if you trip a breaker, both sides are going to trip, but now each breaker will have to be reset individually. It's the same reason two single pole breakers with a handle tie don't make a two pole.
 
OP
C

caleb90

Well-known member
Joined
Apr 12, 2020
Messages
54
Location
at home
Its a square d breaker. Must not be internal as i took that tie off. Shut the one side to off and the other to on and i have 120 to the shed
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,253
Location
Coastal NJ
Its a square d breaker. Must not be internal as i took that tie off. Shut the one side to off and the other to on and i have 120 to the shed
You would have to trip one side not just turn it off to know if there is an internal common trip. Trip is different than switching off.

The handle tie you removed provides common switching.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,991
Location
Modesto, CA
do you have a main disconnect in the shed subpanel? did you isolate the neutral bus from the enclosure? install 2 ground rods?
 