That setup makes a lot more sense
It certainly should. Look at eh diagram on the inside of the door, is should how the panel works. Those lugs on the bottom are to feed a sub.So I guess I was not remembering correctly that the 200A breaker only turned off the garage. It looks like it would just turn off everything.![]()
The panel is dated 2021, so definitely should be 4 wireIt certainly should. Look at eh diagram on the inside of the door, is should how the panel works. Those lugs on the bottom are to feed a sub.
Btw if this was recent work, the house and the garage likely should have been fed with 4 wires
Probably, I know there's some weird code implementation in a few areas though.The panel is dated 2021, so definitely should be 4 wire
If the garage has six breakers or less, it's fine codewise but whoever installed it is a ***** for not putting a main in.So should I have a way to cut off the garage for code? The panel at the garage does not have a main cutoff, just two rows of breakers.
Fed from that main panel underground then through the wall into this panel. No disconnect between.This is fed directly from the original panel you posted, with no other panel, disconnect or box in between?
That's like the wrong wire in several ways...
Does this go underground?
Would a 20a be enough for that surge protector to work? Wanted to have more than 100A to the garage. I don't know what that aluminum wire gauge is for the garage run, but do you think I could put in a 125A breaker for it (a pro would do that, as the POCO would have to pull the meter for working on the panel)?How did the ser cable transition to individual conductors between panels?
- Remove the spd leads from the 100a cb.
- Move the garage feeder to the 100a cb.
- Remove the homeline cb.
- Add a 2pole 20a siemens cb, connect the spd and recept to it.
Since the wire in the garage looks like #2 SER to me and it's officially only rated for 90 amps for this usr, that won't work too well if I'm right. Right now, since it begins outside, it's ok to be fed from the 200 amp lugs but should be landing on a 90 amp breaker or fuses at the garage, but I wouldn't lose any sleep over a 100 amp main.Would a 20a be enough for that surge protector to work? Wanted to have more than 100A to the garage. I don't know what that aluminum wire gauge is for the garage run, but do you think I could put in a 125A breaker for it (a pro would do that, as the POCO would have to pull the meter for working on the panel)?
The outside panel neutral is bonded on upper right side with green screw.Since the wire in the garage looks like #2 SER to me and it's officially only rated for 90 amps for this usr, that won't work too well if I'm right. Right now, since it begins outside, it's ok to be fed from the 200 amp lugs but should be landing on a 90 amp breaker or fuses at the garage, but I wouldn't lose any sleep over a 100 amp main.
WTF? A three wire feeder at the main, four wire feeder at the garage, ground landed on the neutral bar and the bonding screw or strap isn't visible to me. Where is the ground coming from? I see a lug that is probably TEK screwed to the can, but has a ground from a smaller SER cable landed on it, and another SER ground is on the neutral bar. And I can't find the third one, maybe it's cut off.
That's a mess that was installed by an incompetent nincompoop. And he probably has a license.
My comment was about the inside panel. Where does the feeder ground originate? It's definitely on the neutral bar, but I doubt there is anything at the other end. There is a three wire feeder leaving the main panel and somewhere there is a transition from individual conductors to the SER. I'm wondering if the three XHHW's stuffed into the Carflex at the pole go into a Jbox on the back of it, out of sight in the picture and it's SER underground to the garage?The outside panel neutral is bonded on upper right side with green screw.
The inside panel is FUBAR'd with grounds/neutrals. Feeder grd is landed on top left lug of neutral bar!
Could be. OP never responded to my q in post 51 about. There's more to story.My comment was about the inside panel. Where does the feeder ground originate? It's definitely on the neutral bar, but I doubt there is anything at the other end. There is a three wire feeder leaving the main panel and somewhere there is a transition from individual conductors to the SER. I'm wondering if the three XHHW's stuffed into the Carflex at the pole go into a Jbox on the back of it, out of sight in the picture and it's SER underground to the garage?
The picture of the main panel gets too blurry when I zoom in; I want to see the part number and know if it was born a feed through or if it was cobbled together in the field. It looks to me like the lug on the right is too high to allow a two pole breaker to fit. Was a bus stab cut off so the lug could fit? Did the guts get pulled out so a bolt could be inserted through the bus bar?Could be. OP never responded to my q in post 51 about. There's more to story.
Fed from that main panel underground then through the wall into this panel. No disconnect between.
Since the wire in the garage looks like #2 SER to me and it's officially only rated for 90 amps for this usr, that won't work too well if I'm right. Right now, since it begins outside, it's ok to be fed from the 200 amp lugs but should be landing on a 90 amp breaker or fuses at the garage, but I wouldn't lose any sleep over a 100 amp main.
WTF? A three wire feeder at the main, four wire feeder at the garage, ground landed on the neutral bar and the bonding screw or strap isn't visible to me. Where is the ground coming from? I see a lug that is probably TEK screwed to the can, but has a ground from a smaller SER cable landed on it, and another SER ground is on the neutral bar. And I can't find the third one, maybe it's cut off.
That's a mess that was installed by an incompetent nincompoop. And he probably has a license.
The picture of the main panel gets too blurry when I zoom in; I want to see the part number and know if it was born a feed through or if it was cobbled together in the field. It looks to me like the lug on the right is too high to allow a two pole breaker to fit. Was a bus stab cut off so the lug could fit? Did the guts get pulled out so a bolt could be inserted through the bus bar?
I saw that too. The 4 bottom lugs just seemed too odd, to me. The insulator "post" on the bottom right has a piece broken within what OP circled in red.The picture of the main panel gets too blurry when I zoom in; I want to see the part number and know if it was born a feed through or if it was cobbled together in the field. It looks to me like the lug on the right is too high to allow a two pole breaker to fit. Was a bus stab cut off so the lug could fit? Did the guts get pulled out so a bolt could be inserted through the bus bar?
It is a feed thru panel. The diagram on the top of the panel label clearly shows a set of lugs.
(But still looks cobbled in the OP's pic)
It might be that it's nothing more than the angle the photo was taken and everything will fit just fine. I completely missed the feed thru diagram on the cover, I was so concerned with getting the part number that I overlooked the obvious...again.I saw that too. The 4 bottom lugs just seemed too odd, to me. The insulator "post" on the bottom right has a piece broken within what OP circled in red.
All I could find were poor quality pics of plug on neutral style pan, but his still looks cobbled. At the same time, I'm wondering how the 2p 30a plugged on to the stab looking properly seated.
Yep, I didn't notice that either.Certainly the lug on the right neutral bar towards the top is a cobbled adder.
I also see that now. It's probably stuffed in the flex as well, making sure there are no wasted cubic inches.Im able to follow the bare neutral wire from the left neutral bar towards the lower right nmfc with the other 3 conductors. I can see a trace of it in about the center of the panel.
Maybe that's a field definition of compact conductors?It's probably stuffed in the flex as well, making sure there are no wasted cubic inches.
Even simpler, just use the 100a cb (actually should be 90a.) That just involves moving wires.So it's feed thru like I mentioned in my last post.
If it was mine I'd want a fused disconnect in the garage to at least be able to shut that panel off without everything else. I'd also want a competent electrician to come in and correct all the stuff going on, NOT whoever did the initial install.
those dont look like factory feed thru lugs.
Main's breaker replaced. Garage moved to 100A breaker, 20A breaker upgraded to dual dual![]()
No wonder:
Is the quad breaker in the lower left listed for the panel? The others are Siemens. But the quad looks different. CH or Eaton BR maybe? I can’t read the label.
Or lord Jesus. All units return to station, stow all gear. All hands now stand down.I mean turn off.
The weatherhead was replaced awhile back due to it being in poor shape. But I can't recall if that was done after the meter/panel upgrade was done or at the same time.a lot better now...
looks like water was getting into it. did someone leave the door open?
Uncertain, didn't see the panel open after it was finished. Photo was from electrician. But it's better than the D square that was in thereIs the quad breaker in the lower left listed for the panel? The others are Siemens. But the quad looks different. CH or Eaton BR maybe? I can’t read the label.