ishiboo
Well-known member
I am installing a new 200A main panel, and have a couple questions. This is in a basement with a stone foundation, so I will be building a 2x4 wall in front of it and mounting a piece of 1/2" ply with moisture barrier to the backs.
1. My plan is to built a 4' wide wall, with a 24" center cavity for the load center and an area on each side to act as a wire chase so I can staple the wires and they will reach the ceiling. The panel will be mounted to the back of the plywood so in the future, a future wall can be drywalled and the panel will be recessed. What prevents this from being declared a raceway/conduit and being subject to derating/conduit fill? Can the top plate be "open" or must I have a top plate with many holes to get around this?
2. The panel is a 200A Homeline. There are ground bus bar locations on each side - is it okay to install both ground bars? I don't see this detail in the specs, but I believe it is.
3. The panel will be fed initially by 2-2-4 service entrance cable. I have 100A main breaker in an outdoor enclosure below the meter. In the future, I will be trenching electrical to the barn and the barn will supply power to the house. Is 2" conduit sufficient to account for this future (4/0 4/0 4/0 2/0 I assume) service? The conduit will enter the back of the panel (not the top) and I will need to make a turn via a LB to direct towards the ground. The bigger the conduit the worse it looks on the outside of the house, or I'd go 2.5".
4. Any best practices/forethoughts you have in a new panel installation?
I will have a 30A transfer breaker with the interlock kit initially, but in the future when the power is fed from the barn there will be an ATS there. I may need to add some load relays at the house but my plan is to put those, as well as things like a whole home surge protector, timers, etc. to the left and right cavities next to the panel.
This panel will feed an old 100A panel serving the 1st floor whose circuits will be gradually rerouted into the new panel (after removing the ground/neutral tie of course), as well as a new 100A QO panel on the second floor.
1. My plan is to built a 4' wide wall, with a 24" center cavity for the load center and an area on each side to act as a wire chase so I can staple the wires and they will reach the ceiling. The panel will be mounted to the back of the plywood so in the future, a future wall can be drywalled and the panel will be recessed. What prevents this from being declared a raceway/conduit and being subject to derating/conduit fill? Can the top plate be "open" or must I have a top plate with many holes to get around this?
2. The panel is a 200A Homeline. There are ground bus bar locations on each side - is it okay to install both ground bars? I don't see this detail in the specs, but I believe it is.
3. The panel will be fed initially by 2-2-4 service entrance cable. I have 100A main breaker in an outdoor enclosure below the meter. In the future, I will be trenching electrical to the barn and the barn will supply power to the house. Is 2" conduit sufficient to account for this future (4/0 4/0 4/0 2/0 I assume) service? The conduit will enter the back of the panel (not the top) and I will need to make a turn via a LB to direct towards the ground. The bigger the conduit the worse it looks on the outside of the house, or I'd go 2.5".
4. Any best practices/forethoughts you have in a new panel installation?
I will have a 30A transfer breaker with the interlock kit initially, but in the future when the power is fed from the barn there will be an ATS there. I may need to add some load relays at the house but my plan is to put those, as well as things like a whole home surge protector, timers, etc. to the left and right cavities next to the panel.
This panel will feed an old 100A panel serving the 1st floor whose circuits will be gradually rerouted into the new panel (after removing the ground/neutral tie of course), as well as a new 100A QO panel on the second floor.