In a main breaker panel, is the neutral buss supposed to be bonded to to the ground bus?

Is the box itself supposed to be bonded to the ground bus?

Seems to me the neutral bus is not supposed to be directly bonded to the box itself, but to the ground bus, then to the box.

The reason I ask is a buddy was asking. He told me he checked voltage from the main to the breaker box and got like 10 volts. I was under the impression he should see 120 volts, just like measuring to neutral. He wasn't sure the box was grounded. The house is about 15 years old and he did mention that the neutal and ground wires were sharing the same bus bar. It seems to me his box is not grounded.

Any sparkies want to clear this up?
 
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
Need more details but in general a main panel has ground and neutral bonded, and it is technically the neutral buss that gets bonded to the ground/panel.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
As long as it is the first means of disconnect the neutral and ground are bonded.

Are there any grounds going to a water line, rods or a ufer?
 

loganb

ALLIANCE MEMBER
Joined
Dec 29, 2011
Messages
5,702
Location
Omaha, NE
As said above...it's the first means of disconnect off the service where the bonding of neutral to ground occurs. If there is a disconnect at the meter before it goes to the "main" panel at the structure...that generally means it's bonded at that disconnect and must remain separate at all panels after that
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,324
Location
Coastal NJ
In a main breaker panel, is the neutral buss supposed to be bonded to to the ground bus?

Is the box itself supposed to be bonded to the ground bus?

Seems to me the neutral bus is not supposed to be directly bonded to the box itself, but to the ground bus, then to the box.

The reason I ask is a buddy was asking. He told me he checked voltage from the main to the breaker box and got like 10 volts. I was under the impression he should see 120 volts, just like measuring to neutral. He wasn't sure the box was grounded. The house is about 15 years old and he did mention that the neutal and ground wires were sharing the same bus bar. It seems to me his box is not grounded.

Any sparkies want to clear this up?
If the neutral and ground wires are sharing the same bus in the main, that's normal.

It seems you are saying there is possibly an elevated voltage on the steel box itself. Is that correct?
Measure voltage from the steel box to the ground/neutral bus and confirm it to be zero.

Once confirmed, you should see 120V from each of the 2 service legs to ANY of the following:
Neutral
Ground
Box.

And ZERO between any two of the following: neutral, ground and box
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,112
Location
Central Iowa
In a main breaker panel, is the neutral buss supposed to be bonded to to the ground bus?

Is the box itself supposed to be bonded to the ground bus?

Seems to me the neutral bus is not supposed to be directly bonded to the box itself, but to the ground bus, then to the box.

The reason I ask is a buddy was asking. He told me he checked voltage from the main to the breaker box and got like 10 volts. I was under the impression he should see 120 volts, just like measuring to neutral. He wasn't sure the box was grounded. The house is about 15 years old and he did mention that the neutal and ground wires were sharing the same bus bar. It seems to me his box is not grounded.

Any sparkies want to clear this up?

The neutral comes from the factory isolated. There is a bonding screw or jumper that needs to be installed which will bond it to the panel. Additional ground bars will be bonded through the mounting screws.

There should be 120 from hot to panel. Since the grounds and neutrals are landed on the same bar, it's a fairly safe bet to say this is the main panel. The bonding screw might not be installed. Sometimes they are stuck in the hole but not run in from the factory. Have him put a screwdriver on the green screw and see if he can tighten it up. At 15 years old, I doubt it has a bonding strap, but if there isn't a green screw, have him check for a phony little metal tab that would land on the neutral and then bend around to a screw in the panel. One time I had a bonding screw that wouldn't get tight, I used a ground bar and a piece of #4 copper from it to the neutral to git 'r done. He also might just need to scrape some paint away. Have him try measuring voltage from a hot to a cover screw hole.

Everyone stating the the first means of disconnect needs to have the neutral and ground bonded are almost right. It's the first point of over current protection, and that is USUALLY also the first means of disconnect, but not always. And, even if it is the first point of overcurrent protection and the first means of disconnect, something mechanical (usually a bonding screw) has to be installed to bond the panel itself to the neutral. All the ground wires in the world landed on the neutral bar isn't going to cause a meter to see 120 volts from hot to the metal of the panel.
 
Last edited:

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,112
Location
Central Iowa
Interesting. I've never seen this distinction mentioned.

Thanks
The only places I can think of where it matters is POCO supplied disconnects, especially REC's. They have pole top disconnects and sometimes they set transformer with customer access to the load side terminals and there will be a non fused disconnect built in to that. I vaguely remember a long time ago it seems like we installed a non fused disconnect for a multi meter service ahead of the meters. Each tenant space then had a meter with a main breaker outside and each of those was then bonded.
 
OP
P

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,877
Location
Fargo, ND
It seems you are saying there is possibly an elevated voltage on the steel box itself. Is that correct?
Measure voltage from the steel box to the ground/neutral bus and confirm it to be zero.
I am assuming it is some weird stray voltage that his VOM is picking up.

Line to the box was 10 and 14 volts depending on which leg he measured from.

Once he bonds the box to the ground I am fairly certain it will go away.
 
OP
P

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,877
Location
Fargo, ND
The neutral comes from the factory isolated. There is a bonding screw or jumper that needs to be installed which will bond it to the panel. Additional ground bars will be bonded through the mounting screws.
I assume the boding strap or screw was never attached or run in.

I also assume the voltage he is reading from line to the box is just stray voltage that his VOM is reading. Once the ground is bonded it will go away.
 

MBfreak

MEMBER EMERITUS
Joined
Dec 10, 2010
Messages
2,301
Location
Linkoping , Sweden
Floating metal box? Can that really be code compliant.
I admit that I know absolytely nothing about US domestic electricity and rules and regulations for same.
Bot tons more of electrical circuits.
Som kind of box internal insulation fault can energize the metal box and offer a surprise to whoever touches the box.

Ola
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,324
Location
Coastal NJ
Floating metal box? Can that really be code compliant.
I admit that I know absolytely nothing about US domestic electricity and rules and regulations for same.
Bot tons more of electrical circuits.
Som kind of box internal insulation fault can energize the metal box and offer a surprise to whoever touches the box.

Ola
It's not compliant. There is likely a missing bond (screw) between the box and the neutral/ground buss.
 
OP
P

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,877
Location
Fargo, ND
The neutral comes from the factory isolated. There is a bonding screw or jumper that needs to be installed which will bond it to the panel. Additional ground bars will be bonded through the mounting screws.

There should be 120 from hot to panel. Since the grounds and neutrals are landed on the same bar, it's a fairly safe bet to say this is the main panel. The bonding screw might not be installed. Sometimes they are stuck in the hole but not run in from the factory. Have him put a screwdriver on the green screw and see if he can tighten it up. At 15 years old, I doubt it has a bonding strap, but if there isn't a green screw, have him check for a phony little metal tab that would land on the neutral and then bend around to a screw in the panel. One time I had a bonding screw that wouldn't get tight, I used a ground bar and a piece of #4 copper from it to the neutral to git 'r done. He also might just need to scrape some paint away. Have him try measuring voltage from a hot to a cover screw hole.

Everyone stating the the first means of disconnect needs to have the neutral and ground bonded are almost right. It's the first point of over current protection, and that is USUALLY also the first means of disconnect, but not always. And, even if it is the first point of overcurrent protection and the first means of disconnect, something mechanical (usually a bonding screw) has to be installed to bond the panel itself to the neutral. All the ground wires in the world landed on the neutral bar isn't going to cause a meter to see 120 volts from hot to the metal of the panel.
The plot thickens.
His meter sits in his yard. There is a breaker panel at the meter with two breakers, one for house and one for his shop. It also has a couple breakers for outlets mounted at the meter. Would this be considered his main panel and the house and shop panels sub panels?

If so and considering the house is 15 years old, pus the ground and neutral wires in the panel are sharing bus bars. I was thinking the box needs to be grounded, no question. Back in 2006 was it approved to share neutral and ground on the same bus? Then bond that mixed bus to the box?

Would it be reasonable for him to update the wiring and separate the neutral and ground wires and then bond the panel to the ground buss?

My understanding in a sub panel you have a ground buss and a neutral bus and they are not bonded in the sub panel. but they are in the main panel.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,220
Location
NJ
Pics of all panels opened will probably be the easiest way to determine cause and remedy.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,112
Location
Central Iowa
The code changed in 2008. A 2006 house could very well have a three wire feeder which would require the neutral in the house panel to be bonded. Since there are neutrals and grounds on the same bar, I suspect this is the case. Photos would help, but are there three or four wires feeding the panel? If four, the neutral should be isolated and separate ground bars put in. If three, everything can be lumped together, but some sort of mechanical bond needs to happen.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,186
Location
Modesto, CA
Floating metal box? Can that really be code compliant.
I admit that I know absolytely nothing about US domestic electricity and rules and regulations for same.

Bot tons more of electrical circuits.
Som kind of box internal insulation fault can energize the metal box and offer a surprise to whoever touches the box.

Ola
nope its not compliant. the bonding is missing...
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,186
Location
Modesto, CA
The neutral comes from the factory isolated. There is a bonding screw or jumper that needs to be installed which will bond it to the panel. Additional ground bars will be bonded through the mounting screws.
Ive seen meter mains with neutral bars that are bolted to the enclosure. no bonding screw or strap needed
 
OP
P

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,877
Location
Fargo, ND
Well, all is good again. I had a discussion with my buddy and it seems the neutral/ground bus was bonded to the box. He just doesn't know you need a bare metal surface for your probe to measure voltage!

He went back and looked at both panels and found the bonding screw/jumper and checked voltage from the mains to a bare spot, (screw hole) and he gets the same reading as measuring to the neutral bar.

I told him to stop F'ing with stuff that isn't broke! :ROFLMAO:

This whole thing started when he decided to tighten terminal screws and then he started measuring voltages.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
He just doesn't know you need a bare metal surface for your probe to measure voltage!


I told him to stop F'ing with stuff that isn't broke! :ROFLMAO:

This whole thing started when he decided to tighten terminal screws and then he started measuring voltages.

Sounds like he absolutely needs to stay away from electrical work.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,112
Location
Central Iowa
Well, all is good again. I had a discussion with my buddy and it seems the neutral/ground bus was bonded to the box. He just doesn't know you need a bare metal surface for your probe to measure voltage!

He went back and looked at both panels and found the bonding screw/jumper and checked voltage from the mains to a bare spot, (screw hole) and he gets the same reading as measuring to the neutral bar.

I told him to stop F'ing with stuff that isn't broke! :ROFLMAO:

This whole thing started when he decided to tighten terminal screws and then he started measuring voltages.
There should be 120 from hot to panel. Since the grounds and neutrals are landed on the same bar, it's a fairly safe bet to say this is the main panel. The bonding screw might not be installed. Sometimes they are stuck in the hole but not run in from the factory. Have him put a screwdriver on the green screw and see if he can tighten it up. At 15 years old, I doubt it has a bonding strap, but if there isn't a green screw, have him check for a phony little metal tab that would land on the neutral and then bend around to a screw in the panel. One time I had a bonding screw that wouldn't get tight, I used a ground bar and a piece of #4 copper from it to the neutral to git 'r done. He also might just need to scrape some paint away. Have him try measuring voltage from a hot to a cover screw hole.
I always try to start with the simple things. It doesn't always work out, but I don't want to be the guy that sets off the parts bomb when I've overlooked the obvious.
 
OP
P

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,877
Location
Fargo, ND
I always try to start with the simple things. It doesn't always work out, but I don't want to be the guy that sets off the parts bomb when I've overlooked the obvious.
Same here, but he is hundreds of miles away, otherwise I would have been looking over his shoulder. He is usually smarter than this!
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,186
Location
Modesto, CA
Well, all is good again. I had a discussion with my buddy and it seems the neutral/ground bus was bonded to the box. He just doesn't know you need a bare metal surface for your probe to measure voltage!

He went back and looked at both panels and found the bonding screw/jumper and checked voltage from the mains to a bare spot, (screw hole) and he gets the same reading as measuring to the neutral bar.

I told him to stop F'ing with stuff that isn't broke! :ROFLMAO:

This whole thing started when he decided to tighten terminal screws and then he started measuring voltages.

Thats a good way to screw up terminations
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,324
Location
Coastal NJ
Nobody wants to have a screw loose.

It the terminal screws were torqued properly at install, they are best left alone.

It’s ok to put a driver on one and confirm it is tight but giving them a twist to be sure they are damn tight can crush a conductor beyond the intended design. If you repeat that process enough times the conductor can shear off.
 
Last edited: