Main Panel on Metal Building

dirtrunner0519

Well-known member
Joined
May 9, 2012
Messages
399
Hi,

I have searched the forum and found a few threads that have sub panels located on the metal building but nothing with an over head feed coming in.

Looking for some input/idea's how to do this. I need to get it done ASAP. I NEED POWER..
 
To avoid these ads, REGISTER NOW!

Whynot52

Member
Joined
Jan 1, 2018
Messages
17
Location
Alabama
First you will need to find out from power company what their specifications are. Here I was required a minimum of 12' clearance from ground to weather head for pedestrian only traffic (15' for drive traffic) and they required meter base center between 4-5 feet from ground. Once that was established i mounted my (power company supplied) meter base on the shop wall that was facing the power pole already in the yard. I fixed the base directly through the wall into one of my 6'x6' post then used a 2" conduit to connect to a 200a main panel that I mounted next to the base. Measured off my rigid 2" conduit for my weather head and mounted it on top of the meter base and fastened it up the wall into that 6x6 post also (check to see if your jurisdiction has strapping space requirements) ....from there you just pull your wires and done.
 

Attachments

  • IMG_0333.jpg
    IMG_0333.jpg
    138.1 KB · Views: 73
  • IMG_0311.jpg
    IMG_0311.jpg
    136.3 KB · Views: 69
  • IMG_0336.jpg
    IMG_0336.jpg
    133 KB · Views: 66
OP
D

dirtrunner0519

Well-known member
Joined
May 9, 2012
Messages
399
Here is the side of the building were i would like to mount it. Currently the eve is 25' above grade.
 

Attachments

  • IMG_6969.JPG
    IMG_6969.JPG
    112.1 KB · Views: 32
  • IMG_6968.JPG
    IMG_6968.JPG
    100 KB · Views: 31

nsula_country

Well-known member
Joined
May 23, 2013
Messages
1,534
Location
Northwestern Louisiana
Like WhyNot52 did is about textbook. Unistrut works wonders in this application. WhyNot52's building was wood pole barn and used a vertical support. Yours appears to be steel frame, this will not work. Attach unistrut to red iron and if required to the metal with bolts and washers. Use silicone to seal.

Thought about attaching pic of mine, but it comes in underground...

You mentioned ASAP. You can get your work in in a day. Then it's usually a waiting game for the POCO.

CT
 
Last edited:
To avoid these ads, REGISTER NOW!

nsula_country

Well-known member
Joined
May 23, 2013
Messages
1,534
Location
Northwestern Louisiana
First you will need to find out from power company what their specifications are. Here I was required a minimum of 12' clearance from ground to weather head for pedestrian only traffic (15' for drive traffic) and they required meter base center between 4-5 feet from ground. Once that was established i mounted my (power company supplied) meter base on the shop wall that was facing the power pole already in the yard. I fixed the base directly through the wall into one of my 6'x6' post then used a 2" conduit to connect to a 200a main panel that I mounted next to the base. Measured off my rigid 2" conduit for my weather head and mounted it on top of the meter base and fastened it up the wall into that 6x6 post also (check to see if your jurisdiction has strapping space requirements) ....from there you just pull your wires and done.

I have to ask... Why did you place your load center outside? Did code/insurance dictate an external disconnect and you chose not to install an unfused disco? Just curious...

CT
 
OP
D

dirtrunner0519

Well-known member
Joined
May 9, 2012
Messages
399
I have to ask... Why did you place your load center outside? Did code/insurance dictate an external disconnect and you chose not to install an unfused disco? Just curious...

CT

Note quite sure what you are asking but i will try to answer.

The panel for the house is in a Mechanical Room inside the house, this is the main feed from the service provider. I asked for a meter spot and they said that the location i want it at is acceptable.

This panel feeds the house via 3" 2/0 underground conduit.

As for as clearance requirements i have read, and will re-read what they are looking for. Strapping at 24" min, 12' overhead clear for walking 18' for vehicle, this is from top of grade per their design requirements.
 

Whynot52

Member
Joined
Jan 1, 2018
Messages
17
Location
Alabama
I have to ask... Why did you place your load center outside? Did code/insurance dictate an external disconnect and you chose not to install an unfused disco? Just curious...

CT

Local requirements for disconnect outside...the meter is “technically” a disconnect but can carry up to a $500 fee if used as one (locally)...so the main outside is pretty much a large over priced disconnect that I could utilized the space with 220 breakers. It’s actually a 200a Main with lugs on bus outside then jumps to a 100a main inside. I have my 220’s outside and 110’s inside...
 
OP
D

dirtrunner0519

Well-known member
Joined
May 9, 2012
Messages
399
I will have a 320A service with 200A going to the house leaving the garage with 120A. This should be enough for me to run everything i want.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,715
Location
NW Iowa
I will have a 320A service with 200A going to the house leaving the garage with 120A. This should be enough for me to run everything i want.

Does your utility not allow 2-200a main breakers on a 320a self contained meter? Unless they don't allow it I would run the two 200's, it will cost almost the same amount.
 
Last edited:
OP
D

dirtrunner0519

Well-known member
Joined
May 9, 2012
Messages
399
Not sure, they consider anything above 320A to be commercial, thus we limit the power to 320A.
 