main panel to sub panel wiring

F3RR3T

Active member
Joined
Feb 7, 2010
Messages
39
Ok well i just upgraded the service in the house from 100amp to 200amp and replaced the main box and all the breakers. (let me know how i did)

Anyway i want to run all my tools in the shop off a 100amp sub panel. Well as you can see i have no where to put a 100 amp breaker. So i was wondering if i can tap the mane buss bars in the panels (where the green arrows are in my picture) with some copper terminals, and run my 4awg from my panel from there.

DSCF0058.jpg
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Should have bought a 40/40 panel instead of a 30/40 panel. The panel will have some special slots for tandem breakers (or possibly any space is OK, depends on the panel).

But yes, replace two of the breakers with two tandems, and the two full width slots you need will open up. Looks like you need to do this at the bottom.

Panel is not designed to be tapped at the point you are indicating, and if you did, you would have to use heavier cable (4/0 aluminum or 3/0 copper) as the only thing protecting the subfeed would be the 200 amp main breaker. cannot use undersized wire.

The 4 gauge (copper I assume) you propose to use is not suited for 100 amps.

Charles
 
Last edited:

StumpFJ40

Well-known member
Joined
Mar 11, 2008
Messages
82
Location
NOVA
This seems to be my standard contribution lately: Take a look at the panel door, it often has a schematic that shows where on the panel you can put the tandem breakers (they allow you to put two circuits in the space of one breaker).
Yep, I've learned just enough to be dangerous:shocking:
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
You need to get rid of that 2 pole Homeline breaker and put a Siemens in. I see one white wire on a breaker that's not reidentifed. Other than that, looks good.

I would of bought a 40/40 panel in your case. I hate using twin breakers on a new install.
 
To avoid these ads, REGISTER NOW!
OP
F

F3RR3T

Active member
Joined
Feb 7, 2010
Messages
39
went and got 2 tandem breakers, and 4 awg should be fine to run 100 amp sub-panel correct the wire run is only 3 feet
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
went and got 2 tandem breakers, and 4 awg should be fine to run 100 amp sub-panel correct the wire run is only 3 feet

no. need #3 copper or #1 AL for 100a. just put your #4 (if its copper) on a 90 amp breaker. looks like you have some MWBCs in there, be careful you dont put both hots from one on the same phase when you are swapping breakers around and installing the tandems.
 
OP
F

F3RR3T

Active member
Joined
Feb 7, 2010
Messages
39
no. need #3 copper or #1 AL for 100a. just put your #4 (if its copper) on a 90 amp breaker. looks like you have some MWBCs in there, be careful you dont put both hots from one on the same phase when you are swapping breakers around and installing the tandems.

mwbc?
and ill just pick up some #3 copper from the borg today
 