Main to sub panel for garage

bkkiller1

New member
Joined
Nov 7, 2019
Messages
2
Location
Appomattox, va
I have a 200 amp main that goes to my 200 amp house panel. I have an open space in the 200 amp main that I could put a 100 or 125 breaker to run to my garage, the panel I have for the garage is a 100 amp service panel. Will this be ok to do. the only other breaker in my main is a 20 amp that runs my well pump.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,268
Location
Modesto, CA
Is the garage attached or detached?

No point in using a 125a breaker for a 100a sub

You need to check your main breaker panel label to see what the max breaker size is.
 
OP
B

bkkiller1

New member
Joined
Nov 7, 2019
Messages
2
Location
Appomattox, va
Is the garage attached or detached?

No point in using a 125a breaker for a 100a sub

You need to check your main breaker panel label to see what the max breaker size is.

Thanks I'll check the main the garage is detached I have to run approx 100 ft to get to the box in the garage
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,353
Location
Alexandria, VA
If it is a detached garage, you will find the most common recommendation is to use 2-2-2-4 AL Mobile Home Feeder (MHF) in trenched conduit and a (max) 90 amp breaker at the main panel. If its inside the house you could use 2-2-2-4 SER cable. It is a very common cable size, so its available from multiple sources for a reasonable price. The only downside is that it can only handle 90 amps.

You can use your 100 amp panel to get more breaker spaces, but the 90 amp breaker at the main will keep you code compliant. MHF is available dual rated, so it can be buried outside and run in conduit (required) inside the house. SER cable cannot be buried or run in a wet area.

Bruce
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,268
Location
Modesto, CA
If it is a detached garage, you will find the most common recommendation is to use 2-2-2-4 AL Mobile Home Feeder (MHF) in trenched conduit and a (max) 90 amp breaker at the main panel. If its inside the house you could use 2-2-2-4 SER cable. It is a very common cable size, so its available from multiple sources for a reasonable price. The only downside is that it can only handle 90 amps.

You can use your 100 amp panel to get more breaker spaces, but the 90 amp breaker at the main will keep you code compliant. MHF is available dual rated, so it can be buried outside and run in conduit (required) inside the house. SER cable cannot be buried or run in a wet area.

Bruce

SER CAN be run in wet areas ABOVE ground.
 
To avoid these ads, REGISTER NOW!

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
It all depends what your going to have connected to that subpanel. Maybe that extra 25 amps would make a difference. If you would go with 125 amps, and being a separate building, You have to have a main in the garage. You would have to probably take a main lug panel, which most are rated for 125 amps, and back feed it with a 125 amp breaker with a hold down kit installed. I have never seen a 125 amp main breaker panel, that doesn't mean they don't exist. Just make sure you size your underground feeders for 125 amps
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,310
Location
NJ
It all depends what your going to have connected to that subpanel. Maybe that extra 25 amps would make a difference. If you would go with 125 amps, and being a separate building, You have to have a main in the garage. You would have to probably take a main lug panel, which most are rated for 125 amps, and back feed it with a 125 amp breaker with a hold down kit installed. I have never seen a 125 amp main breaker panel, that doesn't mean they don't exist. Just make sure you size your underground feeders for 125 amps

That's the hard way and wastes a couple of branch circuit spaces.
Use a 200a rated panel with a 200a main cb. As long as the rating of the panel equals or exceeds the rating of the feeder ocp, the main cb in the panel acts as a disconnect & provides short circuit protection only. The upstream feeder ocp provides short circuit and o/l protection for the feeder.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
That's the hard way and wastes a couple of branch circuit spaces.
Use a 200a rated panel with a 200a main cb. As long as the rating of the panel equals or exceeds the rating of the feeder ocp, the main cb in the panel acts as a disconnect & provides short circuit protection only. The upstream feeder ocp provides short circuit and o/l protection for the feeder.

I see your point, but that would not be legal in my area. Has to be 125 amp breakers at each end.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,310
Location
NJ
I see your point, but that would not be legal in my area. Has to be 125 amp breakers at each end.


Once the feeder and panel is protected one time there is no NEC requirement for further redundant protection.

If a disconnect switch was used before a main lug panel, the requirement of 230.70 is met. Disconnect switch has no ocp provision.

What legally adopted requirement in St. Lou area makes it "not legal"?
 