My brother and my father wired his house when it was built in 2019. Fully permitted and inspected.

Anyhow, they used a fused A/C disconnect inside the house for a small pool. Breaker tripped recently, and my brother thought the pump failed. He opened up the disconnect which was melted inside. One wire was charred, and at least one fuse was welded in place. It appears the terminal holding the wire was not tightened properly.

Amperage requirements were double checked. Wire size and breaker/fuse sizes are correct. Pump is fine after new disconnect installed.
 
To avoid these ads, REGISTER NOW!

driftpin

Well-known member
Joined
Dec 22, 2016
Messages
11,324
Location
Miami-Dade/Broward Co. Florida
The NEC requires terminations be torqued to manufacturers specs.
One of the reasons several years ago, I acted upon a GJ Hot Deal posted. I bought a low-range torque wrench from a Louisiana NAPA store, along with some flare-nut wrenches, and a 3/8" flex-head medium length ratchet. I believe all were at big-discount close-out pricing. I got everything I ordered. SOme other GJ members didn't. I'm thankful for the Hot Deal post.

Now I can torque my breakers correctly and hard-wire connections too. Being a retired fire-rescue f.f./paramedic and fire inspector, I got to see what can result from improperly-torqued connections.
 
OP
R

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,571
Location
Minneapolis, MN
The NEC requires terminations be torqued to manufacturers specs.
I have all of the proper torque tools for myself now. When I asked about torque tools a while back here a number of electricians said they never use torque tools. I will see if my brother wants to borrow the appropriate torque tool.

Inspectors don't seem to care about use of torque tools.
 
OP
R

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,571
Location
Minneapolis, MN
I was incorrect about a new disconnect being installed already. My brother temporarily bypassed the disconnect and the pump worked. He is not going to operate it again until my father is over to help with disconnect replacement.
 

cannuck

Well-known member
Joined
Nov 30, 2021
Messages
4,662
Location
Rural SK
At least OP's loose connection didn't knock down a bridge and kill the workers on the deck. I was the mechanical guy/fastener Nazi around a bunch of HV utility and industrial jobs for many years. You would be surprised and shocked (sorry, electrical pun) at just how many equipment outages happen because of loose/improperly tightened/improperly terminated wiring.
 
To avoid these ads, REGISTER NOW!

Chuckster in NJ

Well-known member
Joined
Jan 26, 2010
Messages
2,331
Location
Hunterdon County NJ
You would be amazed about how many electrical contractors don’t torque their connections let alone MOST don’t even own a torque wrench.
Once I started to talk "freely" to contractors on their jobs (without judgement) I would ask them about torquing connections and most of them said they did them "hand tight" and could not find what the torque requirements are on the connections. The ones that knew about torquing requirements always had a clean "well organized" work truck along with personal arc fault protection stored so it would not get damaged or dirty………. Once I started talking (educating) to these "hand tight/good enough" guys most of them went out and purchased a torque wrench and used it PLUS some wrote the torque values inside the enclosure with a sharpie so when I opened the door I saw the numbers.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,068
Location
NJ
Not all wiring devices have a torque spec stated in the installation instructions.
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,328
Location
Alexandria, VA
Let me make one simple suggestion, even if you don't actually measure the torque. Make sure you use a square bit screwdriver or other tool that is designed for electrical screws. Do not try to use a Phillips or flat-tip screwdriver to get the wire connections tight, even for the wires on a receptacle.

Standard screwdrivers depend on hand pressure into the screw (Phillips) or maintaining the right angle on the tip (flat tip), and in many electrical applications it's hard to get it aligned properly. A square bit makes a firm connection to the screw head, and can be used with a ratchet, torque wrench or a square bit screwdriver. Its much easier to get a good bite and tighten the screw properly.
 

Higgins

Well-known member
Joined
Dec 25, 2009
Messages
1,944
Location
Shepheardsville, KY
Not all wiring devices have a torque spec stated in the installation instructions.
Anything that is mounted within a main panel, or sub panel had the TS stamped on the side of the device, main panel have the TS listed on the large label on the front.

As for electrical sockets i believe the TS are torqued to around 10 - 14 inch pounds. anything within that range should be OK.

AL
 
OP
R

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,571
Location
Minneapolis, MN
Let me make one simple suggestion, even if you don't actually measure the torque. Make sure you use a square bit screwdriver or other tool that is designed for electrical screws. Do not try to use a Phillips or flat-tip screwdriver to get the wire connections tight, even for the wires on a receptacle.
You can still buy breakers that have only slotted screws. I bought four Siemens 125 amp breakers last year that have slotted screws. I found a slotted bit for my inch pound torque wrench that fits the slot perfectly. I have to use a bunch of downward pressure to torque the screws without stripping them.
 