manifold valves and gauges question

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
I am looking into how the knobs work on a manifold, but I am a bit confused by this picture that shows on one of the manuals, with the valves closed, will the gauges still read anything like the picture instruct to do?

I thought you would have to open the A and B valves for the gas to go into the manifold and thus making the gauges read the pressures

attachment.php
 

Attachments

  • Screen Shot 2018-03-09 at 2.44.28 PM.jpg
    Screen Shot 2018-03-09 at 2.44.28 PM.jpg
    19.8 KB · Views: 121
To avoid these ads, REGISTER NOW!

Jeepster04

Well-known member
Joined
Jun 25, 2013
Messages
3,114
From what I understand, you only open the valves to pull a vacuum or add refrigerant.
 
To avoid these ads, REGISTER NOW!

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
The manifold is a plenum. The valves isolate the individual hose ports from the plenum. The gauges are always open to the high side and low side ports to the hoses you hook up to the service valves on the compressor. "A" is the "low" side "B" is the "high" side. "C" is the vacuum port. "D" is the refrigerant port.

Tommy
 
OP
P

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
The manifold is a plenum. The valves isolate the individual hose ports from the plenum. The gauges are always open to the high side and low side ports to the hoses you hook up to the service valves on the compressor. "A" is the "low" side "B" is the "high" side. "C" is the vacuum port. "D" is the refrigerant port.

Tommy

Thanks for the explanation. So for example I need to isolate a nitrogen psi test or vacuum hold. What I have to do is close “A” and the gauges and blue hose will be the only thing connected to the system.

I guess using red gauge and a hose from that side will accommodate higher psi test though.

Mini split don’t have the high side service port at least not in plain sight, so “B” will just be kept closed.
 

bobbyjean

Well-known member
Joined
Aug 25, 2017
Messages
319
Location
hudson valley n.y.
you need to pull a vacuum on line set...the hose's are going to be good for either 800 or 1500 psi...you should be nowhere near that with nitrogen
if your flaring copper..try nylog...have had great luck with it
 