OP, can you help explain the 2 panels: distances from meter, loads, etc.
Does the garage really need to come off of the meter or could it be a sub to one of the 2 existing panels?
Could the second panel become a sub off of the first panel (even if it means upgrading first panel)?
Really need a load calc for each panel, what you consider critical loads, and of course what is planned for garage.
One panel is 30 feet from the meter and the other is about 75 feet. They are each central to about half of the house and everything fans out from them.
Will work on a load calculation for each panel and the garage. I see Mike Holt has a spreadsheet for residential load calculation, is that a good tool to use?
Not liking that ground wire seemingly so close.
May be the angle of the shot, there is at least 1.5" of distance between them.
I don't see any reason to upgrade this service unless the loads in your new building put you over 200A of actual load. Others seem to think that simply adding up breakers somehow equals load. It does not work that way, it is perfectly acceptable to have 3-400A worth of breakers on a 200A service as long as you have determined the load to be less than 200A. This is actually a common practice on much larger services.
Ah, thanks for explaining, that was a piece of info I was missing.
you need to separate out the circuits you want to run off generator
and make a generator fed panel whose load is sized to the generator.
I want the option to try and run anything. Priorities will change over the course of a day, there's not one set of loads sized to my generator that I see running. Additional breaker protection aside, the generator will drop the load to protect itself if it gets too high for it.
OP needs the loads calcs in order to provide enough info in order to understand best way to clean up this breaker mis-match and make gen tie-in easy. Current set-up is a problem.
Agree that we need more info. Will work on load calculations and get the poco to tell me what the existing service drop can supply to a meter base.
This just seems like a problem waiting to happen as the future loads change and no one is looking any further than just plugging in more cb's to the local panel.
Let's not put too much emphasis on that first picture I posted of how I wanted to lay things out. I should have started by stating what I want to do and let the process of "figuring out how to do it" play out. I want a solution that's good for the long haul and doesn't depend on the inspector missing something to pass.
What about a Meter Collar transfer switch from the Utility company to hook up your generator to the entire house?
Good suggestion and very convenient solution, but the poco doesn't allow them. I originally thought of the RV cable as a safe way to power a decent amount of the house from the generator, but it is capable of more than the 50A capacity of the cables/connectors. I've seen it sustain 60A@240V and would ultimately like to be able to get that to the house from a permanent pad. Until I figure out where the pad will be I was thinking the RV cable would be a good temporary solution.
-- Carl