Master Bathroom Remodel

stroked80z28

Well-known member
Joined
Feb 1, 2012
Messages
49
Location
Pierce County, WA
I am currently remodeling the master bathroom in my home and have reached the point where it is time to start rough plumbing. The attached photo shows a window that I just added. The original vent for the two vanities ran right where I wanted the window, so I removed the vent. I will be installing two console sinks approximately 30" wide each, the centerline of the sinks will be approximately 42" off the centerline of the window. This arrangement places the drain for each sink approximately 84" apart. The capped waste line in the photo is 2" ABS. My questions are:

I believe that because of the distance between the sinks, each fixture will need its own vent. Is this correct?

Is there a code required height for the waste lines for the sinks?

Which fitting should I use where the waste lines (1.5") meet the 2" waste line that goes through the floor?

Thanks for your time. More questions and photos to come as I progress or hit a wall. Thanks again.Pre-sink reduced.jpg
 
To avoid these ads, REGISTER NOW!

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,824
Location
Niagara Region, Ontario, Canada
I believe that because of the distance between the sinks, each fixture will need its own vent. Is this correct?

Is there a code required height for the waste lines for the sinks?

Which fitting should I use where the waste lines (1.5") meet the 2" waste line that goes through the floor?
vents cannot be longer than 5' and yes, each sink needs to be vented
if I recall, about 16" off the floor for waste lines
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
I am currently remodeling the master bathroom in my home and have reached the point where it is time to start rough plumbing. The attached photo shows a window that I just added. The original vent for the two vanities ran right where I wanted the window, so I removed the vent. I will be installing two console sinks approximately 30" wide each, the centerline of the sinks will be approximately 42" off the centerline of the window. This arrangement places the drain for each sink approximately 84" apart. The capped waste line in the photo is 2" ABS. My questions are:

I believe that because of the distance between the sinks, each fixture will need its own vent. Is this correct?

Is there a code required height for the waste lines for the sinks?

Which fitting should I use where the waste lines (1.5") meet the 2" waste line that goes through the floor?

Thanks for your time. More questions and photos to come as I progress or hit a wall. Thanks again.Pre-sink reduced.jpg
Just bring up a seperate vent for each above the window,then tie them back together.
 
OP
S

stroked80z28

Well-known member
Joined
Feb 1, 2012
Messages
49
Location
Pierce County, WA
Just bring up a seperate vent for each above the window,then tie them back together.
Sorry, the photo does not illustrate the height of the window on the wall. The ceiling is vaulted and the window is installed on the "short" side of the room. The top of the window is about 9" from the ceiling.
 
OP
S

stroked80z28

Well-known member
Joined
Feb 1, 2012
Messages
49
Location
Pierce County, WA
Sorry guys. Here is another photo that illustrates why connecting vents above the window is not an option.
 

Attachments

  • Pre-sink2.jpg
    Pre-sink2.jpg
    120.1 KB · Views: 115

rancherbill

Well-known member
Joined
Oct 18, 2007
Messages
5,332
Location
Foothills County, Alberta, Canada
OMG flying King and Cripple studs on the left side of the window. You don't see that too often. :):D


How cold is it where you live? Washington has several climates. Drains in an exterior wall can freeze. We had one freeze twice a year.
 

Sturgeon

Well-known member
Joined
Oct 9, 2021
Messages
269
Location
W. Mt.
Run two individual 1 1/2" vent's up into trusses, tie them together and pick up vent going thru roof. Or tie vent's together below window sill but make sure to use drainage fittings on the two vents until above 42". Besides destroying your dill bit by running right under window sill. Other than more work to just go up twice it would in most cases, be easyier and neater. Trap line 18" center off floor, water 22". Fyi, make sure there's not earent nails when you do go thru top plates, never know about those framers.
 
OP
S

stroked80z28

Well-known member
Joined
Feb 1, 2012
Messages
49
Location
Pierce County, WA
OMG flying King and Cripple studs on the left side of the window. You don't see that too often. :):D


How cold is it where you live? Washington has several climates. Drains in an exterior wall can freeze. We had one freeze twice a year.
The photo makes the bottom plate "issue" look much worse than it actually is.

I am located in Western Washington, no issues with prolonged freezing temperatures here most of the time.
 
To avoid these ads, REGISTER NOW!

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,824
Location
Niagara Region, Ontario, Canada
so the vent went thru the roof where the window is? maybe I didn't read the original post as good as I should have... me bad. \but can't you run a vent beside the window and tie in above the window, in the joist or truss bay?
 

Dig Doug

Well-known member
Joined
Apr 16, 2018
Messages
1,094
Is there a 2nd floor above the bathroom ?

if not run up and make the connections in the attic space
not your exact situation

IMG_9347.jpegIMG_9348.jpeg
Easier to see it than try to explain it

you’ll have to make a loop and run up into attic and make the tie in up there then run through the roof structure
 
Last edited:

M.Wong

Well-known member
Joined
May 5, 2021
Messages
71
Location
Seattle, WA
I don't know anything about plumbing but just had a remodel, two sinks with a window, high ceilings.

They have vents one way for the shower and left sink, the other way for the toilet and right sink.

IMG_3973.JPG
 

Dig Doug

Well-known member
Joined
Apr 16, 2018
Messages
1,094
No second floor and no attic.
Crawl space below?

you can separate / Spit / Wye below the floor or in the wall and run to each sink and just have 2 vents up through the roof line

I noticed the plywood sheeting

splitting it below makes less holes in the studs assuming the waste line is ran below the floor joists ….

There are a few ways to do it….
 
OP
S

stroked80z28

Well-known member
Joined
Feb 1, 2012
Messages
49
Location
Pierce County, WA
Crawl space below?

you can separate / Spit / Wye below the floor or in the wall and run to each sink and just have 2 vents up through the roof line

I noticed the plywood sheeting

splitting it below makes less holes in the studs assuming the waste line is ran below the floor joists ….

There are a few ways to do it….
I also neglected to mention, no crawl space access. Poured slab and sleepers.
 

Dig Doug

Well-known member
Joined
Apr 16, 2018
Messages
1,094
edit -
is there anything else on that line that needs to be vented?

if you don’t know for 100% sure…
I’d add a clean out to outside then then run the pipe up and tie into the new vent above the sink to the closest sink vent

This vent connection needs to at least 6 inch above the flood plane of the sink
The idea is that if the sink gets clogged it will over flow and not just drain back down in the vent from the Wye.

better to be safe than sorry later…

I’m not there BUT - looks great from my recliner!!

@stroked80z28
I edited my 1st reply after some thinking about…. What IF
 
Last edited:
OP
S

stroked80z28

Well-known member
Joined
Feb 1, 2012
Messages
49
Location
Pierce County, WA
Drains installed today and vents tomorrow. Nothing is glued up yet. I plan on venting where the sanitary tees are set. Does anyone see any issues?IMG_2194.jpeg
 