Max amp size to shed?

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,877
Location
NW Iowa
The NEC says I need a 4 wire feeder. If I run 3 wires people claim it's unsafe.

If I have the utility run a service with a separate meter to the same building they will run 3 wires. And there is no safety issue.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,243
Location
Modesto, CA
The NEC says I need a 4 wire feeder. If I run 3 wires people claim it's unsafe.

If I have the utility run a service with a separate meter to the same building they will run 3 wires. And there is no safety issue.
tell me you dont understand neutral currents running on unintended pathways without telling me....
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,877
Location
NW Iowa
tell me you dont understand neutral currents running on unintended pathways without telling me....
I get the reason. Honestly it's less of an issue than it used to be. Most piping is plastic and copper communication lines aren't used as much.

I just don't agree that it's ok for one entity but not ok for another. If it was a big safety issue then all services would need a separate ground
 
OP
4

428PI

Well-known member
Joined
Jul 14, 2018
Messages
1,976
Location
Peabody, KS
Called my niece in law's dad who does electrical to see if he was interested and he said he didn't have a bucket truck. Called a local electrical service and an older gentleman came out that afternoon and looked it over. Said they would do it on ladders. Said they'd run a 3 wire to 100 amp box in my shed. Said it might take 2 months (I said ok the electrical is still working and the concrete won't be done for 2 months anyone). Haven't heard in estimate in almost a week now. Waiting for estimate on framing in the garage door and haven't heard peep from him either. I wonder if the estimators put off giving estimates so the owner doesn't go about getting another estimate? I have heard of people complaining about not getting help to do things and I've run into the same problem with the people complaining. The fact is that everyone only wants to do what's the most profitable to them and easiest. Sometimes you just gotta do the task yourself.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,243
Location
Modesto, CA
Called my niece in law's dad who does electrical to see if he was interested and he said he didn't have a bucket truck. Called a local electrical service and an older gentleman came out that afternoon and looked it over. Said they would do it on ladders. Said they'd run a 3 wire to 100 amp box in my shed. Said it might take 2 months (I said ok the electrical is still working and the concrete won't be done for 2 months anyone). Haven't heard in estimate in almost a week now. Waiting for estimate on framing in the garage door and haven't heard peep from him either. I wonder if the estimators put off giving estimates so the owner doesn't go about getting another estimate? I have heard of people complaining about not getting help to do things and I've run into the same problem with the people complaining. The fact is that everyone only wants to do what's the most profitable to them and easiest. Sometimes you just gotta do the task yourself.
So theyre running a 3-wire feed off a disconnect at the pole?
 
To avoid these ads, REGISTER NOW!
OP
4

428PI

Well-known member
Joined
Jul 14, 2018
Messages
1,976
Location
Peabody, KS
So theyre running a 3-wire feed off a disconnect at the pole?
Act like it's no big deal. I also asked why there was ground at the shop and at the shed and he said most likely because of lightning. The thought was that the buildings needed to be grounded (in particular the steel shed) because of lightning. Like I said there is no inspection done at the county level for any codes.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,243
Location
Modesto, CA
Act like it's no big deal. I also asked why there was ground at the shop and at the shed and he said most likely because of lightning. The thought was that the buildings needed to be grounded (in particular the steel shed) because of lightning. Like I said there is no inspection done at the county level for any codes.
grounding electrodes are for lightning yes. and those are a different animal than an EGC- equipment grounding conductor, from the source panel..... both are required.

you should get a different electrician. this one doesnt know what hes doing.
 