Im trying to figure out the sizing of my sub panel for the 100amp service coming out to my detached garage. Specifically I am questioning how many heaters I can have on a single circuit. Here are the details:
100 Amp sub panel in detached garage 60' from main house panel
Each Marley/Qmark hydronic baseboard heater is 240v and 2,000 watts at 8.6 amps
Instructions say you can hook two of these together in series
I have 6 of these to install across the two separated 25x32 double garage halves, and the two second floor independent 20x20 workshop/storage "rooms"
My plan was to run 12ga copper to two of them off of a dedicated 20amp breaker
Now I am hearing that a 12ga run with 20amp breaker has a max wattage rating of 3,500 watts and 16 amp heater draw?
Help.....how many circuits of what size do I need in the sub panel to operate the Six units? One dedicated 20amp breaker for EACH unit?