It's actually come down a lot in the last couple of years. Still about 20- 30% more than before the "pandemic"Thanks again. It would always remain accessible if I choose to use what I found today plus 25 ft more I would purchase. I had no clue that copper wire had went up that much in price.![]()
You were correct. I think I had that load wire leaving the GFCI bent a little too much.You're fine. The cable leaving the GFI might be bent a little tight, but hard to tell from the picture. The only real code violation is that the bathroom outlet shouldn't be on a circuit with anything other than the bathroom, but I might have installed a receptacle for a freezer on the same circuit as my basement bathroom when I remodeled it about 10 years ago so who am I to judge?
Isn't that a ground rod next to the pipe in the picture? We really don't use water lines or gas lines anymore. Too often plastic is used somewhere and the ground gets lost. I live on solid rock and I drilled mine for four panels six feet down with a concrete drill and packed them with conducting grout. I'm sensitive to lightning strikes since I've been lucky enough to survive 3 times. The power company didn't do a good ground at the pedestal and the transformer headed for the tops of the trees during a strike where I was working on a panel. Our milk cow was struck during a vigorous storm and it bounced off my dad and hit me. The third time I was watching tv in my living room when it hit a tree a couple feet away. All I lost was a finger and some flesh on the foot and shoulder. The other two times, I got burns and an impact injury. A lot of lightning here. A bolt came out of the tv and went through my leg to my desklamp post. So, I think grounding is very important.Thanks. I was thinking because of the green screw that is bonded to panel on the left side of this panel that it was the ground side. Thew other side didn't have this.
I did find the Eaton ground bar but I got to make sure it fits.
As far as the ground wire going to water pipe. I don't know where they would be because I re plumbed this house 30 years ago with CPVC. The # 6 bare copper wire is tied to the ground rod I showed in this picture.
There is a pipe driven in the ground close to ground rod. It may have been tied to water pipes years ago. When I just looked I did notice one small ground wire is broke that I need to connect back. Could have been an old phone line ground that is no longer used.
It was late when I posted and I just edited it and said I would hire an electrician.The 4 wire changeover is the safer route.
However, 250.140(B) (5) requires the bare neutral to be insulated to prevent contact with the sub-panel grounded surfaces as that cable enters the sub-panel and outer jacket removed.
This can be accomplished by taping the conductor or adding sleeving material (shrink tube) along the bare conductor's entire length within the sub-panel until it terminates on a neutral bar.
You still need to add the ground bars, remove the bonding strap from the lefthand neutral bar and move any ground wire currently landed on neutral bars onto the ground bars.
The city just replaced my gas meter with a smart meter and they didn't connect any ground wires to it so they are no longer there.Isn't that a ground rod next to the pipe in the picture? We really don't use water lines or gas lines anymore. Too often plastic is used somewhere and the ground gets lost. I live on solid rock and I drilled mine for four panels six feet down with a concrete drill and packed them with conducting grout. I'm sensitive to lightning strikes since I've been lucky enough to survive 3 times. The power company didn't do a good ground at the pedestal and the transformer headed for the tops of the trees during a strike where I was working on a panel. Our milk cow was struck during a vigorous storm and it bounced off my dad and hit me. The third time I was watching tv in my living room when it hit a tree a couple feet away. All I lost was a finger and some flesh on the foot and shoulder. The other two times, I got burns and an impact injury. A lot of lightning here. A bolt came out of the tv and went through my leg to my desklamp post. So, I think grounding is very important.
I know the 4-wire way would be the best route but it would be tough to get those wires into this panel safely .
Isn't that a ground rod next to the pipe in the picture? We really don't use water lines or gas lines anymore. Too often plastic is used somewhere and the ground gets lost. I live on solid rock and I drilled mine for four panels six feet down with a concrete drill and packed them with conducting grout. I'm sensitive to lightning strikes since I've been lucky enough to survive 3 times. The power company didn't do a good ground at the pedestal and the transformer headed for the tops of the trees during a strike where I was working on a panel. Our milk cow was struck during a vigorous storm and it bounced off my dad and hit me. The third time I was watching tv in my living room when it hit a tree a couple feet away. All I lost was a finger and some flesh on the foot and shoulder. The other two times, I got burns and an impact injury. A lot of lightning here. A bolt came out of the tv and went through my leg to my desklamp post. So, I think grounding is very important.

So you can do as post 46 states.They are