Thanks for the responses, my Sterling model GG 45,000 Btu heater's installation manual under gas piping requirements for natural gas calls for supply inlet pressure 5.0 inch WC min, and 14.0 WC max, with my supply of .25psi (17.5767 WC) is this close enough not to need a pressure reducer ?
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,848
Location
NJ
From my yellow jacket test gauge.....6 osi = 10.4 " wc. You have ~ 7.0"wc.

The real question is, was your reading at the heater while it was fired up or when it was off or fan only?

You want a measurement when the unit is fired up.


You do not need a pressure reducer as your supply pressure is at the low end of the heater spec.

Does the piping to the heater supply other loads? If yes, you may want the other load consuming while you take readings at the heater.
 
To avoid these ads, REGISTER NOW!

HoosierBuddy

Well-known member
Joined
May 9, 2006
Messages
2,915
Location
Southern Indiana
The most common supply pressure for natural gas is when the Gas Company provides the customer with 7-inches w/c, and virtually all NG appliances are built with that in mind.

The reason (if anyone cares) is that residential gas meters are factory calibrated to be accurate at 7-inches w/c (at sea level). Since all gasses are compressible, if they gave you more or less pressure than that, the meter wouldn't be accurate without taking additional steps to correct it....which there are many ways to do...but they all add to cost.

If you live in a high altitude area, your gas company probably provides you with a higher pressure to compensate the metering for the altitude...but that discussion is going to involve math...and it's too early for that.

Phil
 
OP
4

47WDXPW

Well-known member
Joined
Feb 5, 2017
Messages
77
Location
South Jersey
From my yellow jacket test gauge.....6 osi = 10.4 " wc. You have ~ 7.0"wc.

The real question is, was your reading at the heater while it was fired up or when it was off or fan only?

You want a measurement when the unit is fired up.


You do not need a pressure reducer as your supply pressure is at the low end of the heater spec.

Does the piping to the heater supply other loads? If yes, you may want the other load consuming while you take readings at the heater.

My measurement was made at a valve that was left for future use and with out the other appliances in use (house heater-gas stove) I will do it again with them on thanks. What is 6 osi,I have been a pipe fitter for many years and don't remember seeing that measurement.
 
OP
4

47WDXPW

Well-known member
Joined
Feb 5, 2017
Messages
77
Location
South Jersey
So with one burner on medium on the stove and the furnace running a heat cycle my gauge went down to 3oz. Which seems to fit the 3.5 min needed for the Sterling heater gas manifold.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,848
Location
NJ
3 osi = 5.2" h2o. Furnace probably the biggest concern. You got that reading with the heater running or not? It should be with the heater running, otherwise it will be starved.

What zip does that belong to?
 
OP
4

47WDXPW

Well-known member
Joined
Feb 5, 2017
Messages
77
Location
South Jersey
Guys I have an older glass manometer in a U bend configuration does it matter what diameter the tube is for use with a WC for a natural gas heater ?
 