"In a bedroom a neckless or a coin dropped down and over the end of a cord, shorting across the spades of the cord"
I'm not an electrician, (electronics and computers is my vocation) but can't you mount the outlet so that the ground hole is "up" to prevent just such a thing from happening?
You indeed can mount the receptacles with the ground pin on top, this does provide a bit of protection from shorts occurring from dropped metal object, but this is only effective if the cords plugged into the receptacles have grounds. Most items found in a bedroom, such as lamps, clocks/radios, TVs and such are rarely equipped with three prong cordsets. The best advice I can give if this is a concern is to install the receptacles with the ground pin up (or, better yet, with the neutral blade up by mounting the devices sideways) and using a good quality (specification grade or better) receptacle. The better receptacles hold the plugs tighter initially and over time, and pushing the plugs tight to the receptacle minimizes exposed prongs. These days the NEC required Arc Fault Circuit Interrupters (AFCIs) in bedroom branch circuits. These devices don't prevent shorts from happening, but minimize the effects/damage when they do happen.