I a moving our meter and going from overhead to underground. The new meter main will be on the side of our detached garage. The old meter base (no disconnect) is on the side of the house. I have a 200 amp breaker that will feed the 200 amp panel at the house downstream of the old meter base. My question is aluminum wire size. My current thinking is 250 mcm aluminum for the 2 hots and 1 neutral and 2 awg aluminum for the equipment ground. I think 4/0 may be allowed but am not sure since its not rated for the full 200 amps. The new meter main will also feed some circuits in the garage.
I have pulled the permit and what I have installed so far is 2“ schedule 40 conduit through the garage and secured under a ground level deck between the garage and the house. I have also installed the meter main. If I go with the (3) 250 MCM and (1) 2 AWG I’m coming up with a 36% fill on the 2” conduit.
Thanks in advance for advice on this installation.
Meter Main: Siemens MC4040S1200S
SubPanel: Siemens PN4040B1200C
I have pulled the permit and what I have installed so far is 2“ schedule 40 conduit through the garage and secured under a ground level deck between the garage and the house. I have also installed the meter main. If I go with the (3) 250 MCM and (1) 2 AWG I’m coming up with a 36% fill on the 2” conduit.
Thanks in advance for advice on this installation.
Meter Main: Siemens MC4040S1200S
SubPanel: Siemens PN4040B1200C