Anyone with experience on either of these adapters? Looks like the simplest way to meter a seperate rate for EV Chargers or solar.

My POCO just approved these for use this year.
1744419943835.png1744420065100.png

I know there was a xfer switch type adapter several years back but that wasn't approved for use. Looks pretty close to this hardware.
 
To avoid these ads, REGISTER NOW!

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,574
Location
Minneapolis, MN
Doesn't the utility normally provide these? I read they are not cheap.

I did a similar concept. I installed a load side tap inside my meter socket. I had to replace the meter socket as mine was too old to have a provision for a tap. I spent at least $1,000 on the project because I also added an exterior emergency disconnect switch and replaced my load center inside the house. I replaced the load center in the house because it would have been too hard to separate neutrals and grounds in my old load center. With the exterior disconnect switch the main load center is considered a subpanel.
 
OP
M

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,120
Location
NJ
Look like $500 or less.

Wider acceptance than I expected. For the right site conditions, this could cost some jobs/reduce scope.
1744468188945.png
 
OP
M

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,120
Location
NJ
As I read further, evse loads are limited to 32A cont max (even though a 30 or 60A cb is available).

There is a 125A cb for the house panel within the meter (underside). So this works on 100 and 200A services, but it cuts the main panel down to a max available of 125A :wtf:. Looks like a restriction based on CB frame size, maybe other limiting factors.

I see only total grid metering capability. I was expecting 2 channels, for reduced rated rate (EVSE) or net-metering for solar.
1744469841969.png
 
To avoid these ads, REGISTER NOW!
OP
M

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,120
Location
NJ
The $500 won't include hiring a sparky to install it
Nor any other downstream hardware required. This could eliminate certain service upgrades that may have otherwise included in evse or solar installs. Situation specific.
 
OP
M

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,120
Location
NJ
Their website is showing me a much shorter list than that. Only 6 utilities
Unless you live where your local utility has approved it, who any how many doesn't matter. It does show it is starting to gain a wide spread acceptance vs. only 1-2 POCOs.

Customer size of the POCO is another factor.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,262
Location
Richmond, VA
Nor any other downstream hardware required. This could eliminate certain service upgrades that may have otherwise included in evse or solar installs. Situation specific.
Absolutely.

I could see using something like this at my house where an evse would be outside, near the meter, but with a 320a service, it's a no go.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,262
Location
Richmond, VA
Unless you live where your local utility has approved it, who any how many doesn't matter. It does show it is starting to gain a wide spread acceptance vs. only 1-2 POCOs.

Customer size of the POCO is another factor.
My point is that their lists aren't even consistent and adoption is very, very small
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,130
Location
Modesto, CA
My PoCo (non-profit irrigation district in Cali’s central valley) would never allow those… nor would Profit Gouge & Execute (PG&E; large private PoCo in Cali).
 