My new garage and breezeway build is going to include a window that will be a little less than 3.0 feet on the diagonal from the meter socket for underground service. Does anyone know of a NEC code that this would violate? I found Article 230.9 that deal with clearance of open conductors to windows but I cant find one specifically for cable in conduit or specifically for meter socket clearance to windows.
230.9 Clearances on Buildings.
Service conductors and final spans shall comply with 230.9(A), (B), and (C).
(A) Clearances. Service conductors installed as open conductors or multiconductor cable without an overall outer jacket shall have a clearance of not less than 900 mm (3 ft) from windows that are designed to be opened, doors,porches, balconies, ladders, stairs, fire escapes, or similar locations.
230.9 Clearances on Buildings.
Service conductors and final spans shall comply with 230.9(A), (B), and (C).
(A) Clearances. Service conductors installed as open conductors or multiconductor cable without an overall outer jacket shall have a clearance of not less than 900 mm (3 ft) from windows that are designed to be opened, doors,porches, balconies, ladders, stairs, fire escapes, or similar locations.