Meter socket conduit routing question

Marctrees

Well-known member
Joined
Mar 5, 2015
Messages
6,265
Location
TX/LA border - Toledo Bend
Standard 200a Milbank meter socket on residence.

Just the old fashioned 200a size can that holds a meter, nothing else.

The power co has fed from underground and come into bottom leftmost KO and gone straight up then bend to right to line side terminals.

I want to feed a 100a panel by coming out of the left side lowest KO cause overall it would be best end result layout.

A local electrician says "power co doesn't like you to do that", I guess figuring some kinda clearance issue.. but there is plenty of room for the load conductors to cross the line to go out that side KO, especially being only 100a wire.

Electrician sez to go out right side, so no conflict w line wires.

I ask him "Why?" I see no conflict going out the left side, and going out right side doesn't work out well for other reasons.

Did I miss something? Is there a Code issue or something I am not aware of?

Does the POCO have a valid reason ?

I have tried to call them and it seems impossible to get an answer short of having a service guy come out and look.

Marc
 
To avoid these ads, REGISTER NOW!

tyme2par4

Well-known member
Joined
May 16, 2016
Messages
571
Location
NH
POCO doesn't need a valid reason. If that's their rule, it's their rule. They aren't going to change it for you.
But what their reason may be, is if they ever need to service their conductors, they would have to move your conductors first.
 
To avoid these ads, REGISTER NOW!

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
You're assuming there's a "rule" by the POCO only based on some electricians belief. And "doesn't like you to do it that way" is not the same as "thou shalt not do this", in other words, is there really a POCO regulation, or do his lineman buddies just have that preference? I would consult with the POCO directly, as this "rule" doesn't make much sense to me. If there's plenty of room, there shouldn't be any issue with using whatever knockout you want. There certainly isn't any NEC requirement, not that POCO's are bound by that anyway.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,536
Location
Minneapolis
I'm guessing on who is your electric utility, but here's a meter installation detail from Deep East Texas Electric: http://www.deepeast.com/sites/deepeast/files/UNDERGROUND_INSTALLATION.pdf


I can only assume they want to keep any wiring on your side of the meter as far away as possible from their incoming wires. It could be for their convenience so their people don't have to work around them, it could be for safety since there's a possibility for your wires to be energized if they touched, even if the meter was pulled.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
In the 14 years I've been doing electrical I've never had to relocate conduits in the meterbase just because the power co. "may not like it."

"Show me in their service requirements manual where it says that, or else I'm going to do what I want and what I like."
 