mhf to subpanel in pole barn

rinconnick

Member
Joined
Sep 18, 2019
Messages
14
Location
kentucky
I plan on running 2-2-2-4 mhf from my house 200amp service with a 90 amp breaker. The distance is about 200 feet from my house and want to run a 90 amp breaker in the subpanel. Does this sound correct at all?
 
To avoid these ads, REGISTER NOW!

OptionalStop

Well-known member
Joined
Mar 23, 2018
Messages
128
Location
Rochester NY
This is exactly what I did only my run was 175'. 2-2-2-4 MHF from my 200 amp main to 100 amp sub in the shop with 90 amp breaker.

Have not tested, or got it inspected yet though, my build is still on-going.
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,207
Location
SE MI
I plan on running 2-2-2-4 mhf from my house 200amp service with a 90 amp breaker. The distance is about 200 feet from my house and want to run a 90 amp breaker in the subpanel. Does this sound correct at all?
The size of the "main" breaker in the sub does not really matter, but I would want it to trip BEFORE the breaker in the house.

What are your loads?

200’ might be pushing it

Go one size down from 90A in the house. Plenty of cushion.
 
OP
R

rinconnick

Member
Joined
Sep 18, 2019
Messages
14
Location
kentucky
When I posted this I didn’t realize there where a hundred and of the same topics already on the forum. Thanks for input guys
 