Microwave randomly blows circuit breaker?

Bulldog13

Well-known member
Joined
Sep 20, 2007
Messages
1,786
Location
Cape Coral ,FL
Had my garage main breaker panel replaced about 3 months ago…did it mainly because the old panel was I guess a possible fire hazard and I was having trouble getting house insurance here in Florida. So my kitchen microwave is on a 15 amp circuit breaker and randomly trips the breaker? It’s a built in microwave over the range…I called the electrician who installed the new panel and he said it’s probably the microwave going bad? Microwave is maybe 1.5 years old….? I’m not an electrician but could it be a bad breaker or should it be a 30 amp breaker ? Didn’t have this problem before the panel was replaced…Thank for any input..
 
To avoid these ads, REGISTER NOW!
OP
B

Bulldog13

Well-known member
Joined
Sep 20, 2007
Messages
1,786
Location
Cape Coral ,FL
Did you use enough ? Marks at the end of every sentence?

Let's start with basic information, what size is your microwave?
Sorry about the question marks . I am not sure what size the microwave is….. I just assumed since I didn’t have a issue before the panel was replaced , that might be the issue.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,969
Location
VT
Sorry about the question marks . I am not sure what size the microwave is….. I just assumed since I didn’t have a issue before the panel was replaced , that might be the issue.

Over the range or countertop?

You need to know the watts, then you'll know what circuit size you need. Then you need to see what size wire is on that 15A breaker.
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,324
Location
Beautiful Southern Maryland
Is the microwave on its own circuit or are there other things on it ? What model is it ?

When our house was new it only had an exhaust fan and light over the stove and it was on a 15A general circuit with another room and outlets. Some years later I replaced the fan with a built in microwave and used the same circuit. It works fine if nothing else on the circuit is working but if there are a bunch of lights on and my Wife has the iron on it will sometimes trip the breaker. The data tag shows 1480 watts which is 12.3 watts so it is pushing right at the limit. If yours is newer and higher powered it might be more.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,973
Location
Central Iowa
^^ I agree. The range probably had a vent hood above it originally that was powered from a 15 amp lighting circuit. The previous owners took the hood out and replaced it with the microwave. The microwave tripped the breaker often enough that they stuck a 20 amp breaker in place of the original 15 and "fixed" it. Then you came along and bought the house as is, but when you had the panel changed, the electrician saw a 14 gauge wire and used a 15 amp breaker for it, like he should have.

When the breaker trips, does anything else go out with it? If it truly is connected to a lighting circuit, you can help it by limiting anything else that is running when the microwave is being used, especially if that something else is a space heater. The only real fool proof solution is to install a dedicated 20 amp circuit for the microwave, but if the microwave is going bad, that won't fix anything this go round. I had never seen a microwave go bad until about two years ago, then I ran across three of them causing dedicated 20 amp breakers to trip in about a four month time span, so it is possible that the microwave is shot.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,973
Location
Central Iowa
I think it’s connected to our guest bedroom and the only thing running is a ceiling fan.
A ceiling fan is going to add a couple of amps to the total load, that might be enough to put it over the edge. Try running a good extension cord from a known 20 amp circuit to the microwave and give it a couple of days. Even better would be to, if you have one, use an amp meter and check the amount of current being used by the microwave and see if it matches up close to the claimed wattage on the name plate. You can buy some ammeters cheap at the box stores if you're so inclined.
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,311
Location
Dutzow Missouri
Generally, the first thing connected to the black wire in the microwave oven is a 15 Amp fuse that will open the circuit long before a circuit breaker could ever trip for over current.

If a over current fault is in the microwave this fuse had almost certainly been bypassed.

The most likely fault in the microwave is the “monitor circuit” this is several different switches connected to the ovens door when the door is closed power is connected to the timer and high voltage transformer. When the door is opened power is first removed and then a short circuit is put across the HV transformer so it is impossible to make microwaves when the door is open. When the switches get old and gummed up they do not operate as quickly as they should so then power may still be being applied when the shorting switch closes. That should blow the fuse.

Walta
 

Attachments

  • 2024-11-02_13-45-57.jpg
    2024-11-02_13-45-57.jpg
    86.2 KB · Views: 8
Last edited:

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,908
Location
Niagara Region, Ontario, Canada
at the volunteer warehouse, we had a small hot water heater . it was labelled 1440 watts and I think it was a 1 gallon. it was a very small unit, good for hand washing but too small for washing volunteer lunch dishes.
Upgraded to a 6 gal "1500watt " heater . it would blow the dedicated breaker about once per day . after looking for loose connections etc we came to the conclusion it was a weak breaker and had it replaced by our electrician. it hasn't popped for about 8 months .thread here
 
Last edited:
To avoid these ads, REGISTER NOW!

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,311
Location
Dutzow Missouri
Does the breaker tend to trip while it is cooking or when or opening or closing the door?

Test the outlet with another load a heater, hair dryer air frier 1500 – 1800 Watts.

Do you own a clamp on Amp meter?

Walta
 
OP
B

Bulldog13

Well-known member
Joined
Sep 20, 2007
Messages
1,786
Location
Cape Coral ,FL
Does the breaker tend to trip while it is cooking or when or opening or closing the door?

Test the outlet with another load a heater, hair dryer air frier 1500 – 1800 Watts.

Do you own a clamp on Amp meter?

Walta
I don’t have a amp meter…it trips on start up but only randomly…I have a call out to the electrician but no call back yet
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,584
Location
Richmond, VA
Microwave is 2023 model…so I’m leaning towards a bad breaker…I’m not great with electric so I’m not confident digging into the new breaker panel
If it's something you want to learn, a little youtube and watching the sparky you hire can get you there.

If you kill the main, the only hot things are the lugs, which likely have yellow caps on them and if not, you can add them for under $20 (good thing for the sparky to do while he is there, just pick them up at HD)
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,973
Location
Central Iowa
Microwave is 2023 model…so I’m leaning towards a bad breaker…I’m not great with electric so I’m not confident digging into the new breaker panel
Run a cord from a 20 amp circuit to the microwave and give it a few test runs. I thought I fixed a five year old microwave that would randomly trip on start up by running a new circuit to it since the refrigerator was also on the same circuit. A couple of days later it tripped again and by the time I got there, the random trip was no longer random, the microwave was junk. Another time, I ran a 20 amp circuit for a microwave that hadn't even been purchased yet. Upon installation, it had random tripping so I went back with my meter and everything seemed to check out fine so I blamed the breaker and installed a new one under warranty. A couple of days later I got a call that it had tripped again. I went back and checked and luckily, while I was there with the meter on, got a spike of somewhere around 40 amps on start up. Junk microwave. They took it back, got a replacement and all has been well since.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,767
Location
Austin, TX
You run your microwave for 3hrs at a time?
Convection, maybe.

Fair point, but I don't trust manufactures to be quite that precise in terms of timing... Not with an old breaker.

I like the suggestion of throwing a 20A extension on it and see how it does. Or clamp the darn circuit and measure it.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,584
Location
Richmond, VA
Convection, maybe.

Fair point, but I don't trust manufactures to be quite that precise in terms of timing... Not with an old breaker.

I like the suggestion of throwing a 20A extension on it and see how it does. Or clamp the darn circuit and measure it.
3 hrs is a hell of a stretch from most microwave use.

I agree, run on a 20a circuit is what I would recommend for someone who doesn't want to open a panel
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,973
Location
Central Iowa
120V * 15A * 80% continuous = 1440w.. It's right on the margin. I don't count on breakers beyond 80% for any length of time.
For it to be a continuous load, it has to run for more than three hours at a time. Post 25 says it trips on start up, a 15 amp breaker would probably go for a few minutes at 20 amps before it heats up enough to trip.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
Convection, maybe.

Fair point, but I don't trust manufactures to be quite that precise in terms of timing... Not with an old breaker.

I like the suggestion of throwing a 20A extension on it and see how it does. Or clamp the darn circuit and measure it.
i doubt a microwave would last running that long. most are rated for intermittent duty
 