I have a 3 phase 3hp Mill that I am trying to run on a 5hp WNY static converter. The mill starts and runs fine but is tripping the heaters in the mag starter after a few minutes of light use. I let it cool, reset the starter and it trips again after a minute. The heaters are labeled B15.5. Are these the right heaters or what else may the problem be? Should I just break down and buy a VFD for it? I included pictures of the motor plate and starter. Thanks
 

Attachments

  • IMG_20191120_193415.jpg
    IMG_20191120_193415.jpg
    77.3 KB · Views: 16
  • IMG_20191120_193530.jpg
    IMG_20191120_193530.jpg
    84.9 KB · Views: 15
  • IMG_20191120_193452.jpg
    IMG_20191120_193452.jpg
    122 KB · Views: 15
  • IMG_20191120_193457.jpg
    IMG_20191120_193457.jpg
    97.8 KB · Views: 18
To avoid these ads, REGISTER NOW!

metlmunchr

Well-known member
Joined
Sep 10, 2011
Messages
1,289
Heaters appear to be the right size based on motor nameplate amperage.

A static converter is the fastest device ever invented for burning up a machine tool motor. The typical vertical mill motor is a special motor due to shaft configuration, and replacements are seriously expensive.

A friend bought a new horizontal bandsaw with a 2hp 3 phase motor in anticipation that he would move out of his single phase only garage and into a building with 3 phase power in the future. In a year's time he fried 2 motors with a static converter, and the third one burned up shortly after he moved to a location with 3 phase power, indicating the static converter was on the verge of killing that one prior to the move.

That was in the late 90's, and he still runs that saw daily with no further motor problems.

A VFD would be a very good investment for that mill.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,268
Location
Modesto, CA
Static converters are ****.

They start motor powered on all 3 legs then drop out one leg and single phase the motor.

My guess is the voltage is low causing the current usage to go up and thus tripping the overloads

EDIT: do you have a clamp meter you could use to test the current draw on each leg? Also test the voltage.

Without the ability to do so metering, you wont be able to figure out much here.
 
Last edited:

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I've always "heard" that a static has to be at least double the size of the load. I would consider a 3 HP VFD in place of that static unit, if possible.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
A VFD or a single phase motor would be best IMO, the VFD would be the most economical solution.
 
To avoid these ads, REGISTER NOW!
OP
K

kingchevy

Well-known member
Joined
Nov 9, 2007
Messages
247
Thanks for the replies. I don't want to risk smoking the motor, I'm going to get a VFD.
 