ishiboo
Well-known member
Looking for the minimum conduit size for 10/3 UF. Will 1" work?
(Schedule 40)
Run is about 200'.
(Schedule 40)
Run is about 200'.
Why pull UF cable in pipe? Use 10 AWG THWN and save a lot of aggravation.
Why run it in pipe? Can you not get down to minimum depth?
Direct buried wire is for folks that like to do things twice.
It's not a matter of "if" but "when".
I can, I have a sub-soiler I could put it down to GFCI depth with...
The GFCI depth (12") applies to residential circuits of 120V and 20A or less ONLY.
Otherwise it's 24" for direct burial except under concrete, where it's 18"
That'd be fine, it's a 15A circuit. My plan is to put it in conduit though obviously.![]()