Customer is asking for 25ft pigtail #12 Solid to be supplied from each 1A 120V (thus 120W) light fixture. This seems excessive to me. I assume this will be run through conduit. Even if the fixtures are on a 20A circuit breaker, does the single uninterrupted fixture feed from the junction box 25ft away really need to be #12? I was thinking #16 would be fine, #14 at most.
 
To avoid these ads, REGISTER NOW!

malibu101

Well-known member
Joined
Jul 1, 2005
Messages
3,908
Location
Walnutport PA
Customer is paying. Is it code compliant when you leave and get paid?

If yes to the above- Just do it and move on.
 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
Sales quoted fixture price without this information. This isn't really a cost issue - more a common sense/code requirement question. Plus, customer wants quick disconnect at fixture = Molex style. Still researching, but I don't think you can use solid wire on Molex crimp terminals. I'm thinking I would have to find a 5 conductor stab-in disconnect that can handle #12 solid. Fixture has night light and emergency backup - hence the 5 conductor.
 

GRB

Well-known member
Joined
May 6, 2014
Messages
828
Location
SoCal
Any wiring before a hardwired fixture will need to be sized for the breaker so 20A breaker equals 12ga.
 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
Thank you GRB. I may not like the answer, but I accept it. They'll have to accept stranded then as I can't find any 5 pin disconnect that accepts solid.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,775
Location
NW Iowa
In cases like this I'll often be a little bit of a hack and run #14 for whips. Especially with some of the current fixtures that give you very little wiring space.

I have seen listed fixure whips with #18 solid wire. Not that it makes it right to do it in the feild, but as you say sometimes common sense goes a long way.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Any wiring before a hardwired fixture will need to be sized for the breaker so 20A breaker equals 12ga.

Not totally true. Fixture wires and Taps to a light fixture can be smaller than the serving circuit but you have to follow NEC requirements. See NEC 240.5(B) and 240.21(B), 410.117(C)
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
Customer is asking for 25ft pigtail #12 Solid to be supplied from each 1A 120V (thus 120W) light fixture. This seems excessive to me. I assume this will be run through conduit. Even if the fixtures are on a 20A circuit breaker, does the single uninterrupted fixture feed from the junction box 25ft away really need to be #12? I was thinking #16 would be fine, #14 at most.

#16?

The smallest gauge building wire is #14
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
#16?

The smallest gauge building wire is #14

There is 16 AWG TFFN fixture wire but not sure how kosher it is to use it, I would err on the side of caution myself, without being sure code is on my side. The 16 AWG whips may only be OK as a factory assembly.
 

GRB

Well-known member
Joined
May 6, 2014
Messages
828
Location
SoCal
There seems to be lots of discussion about what actually qualifies as fixture wires or whips. I know some inspectors here allow #14 in flex up to 6' and some don't. CA is likely to be picky and LA County more picky.
I should have qualified my answer more but when I saw 25', I didn't think it was necessary.
 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
Yeah, this is the first time anyone has asked for 25'. I was only thinking #16 since that's what we use in cable for ship lighting and heck this is only feeding 1 fixture. #12 still sounds ridiculous to me, but we'll do it. I told sales if the customer wants solid, they'll have to define the 5 pin connector - otherwise they get stranded. (The customer isn't always right.)
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
There is 16 AWG TFFN fixture wire but not sure how kosher it is to use it, I would err on the side of caution myself, without being sure code is on my side. The 16 AWG whips may only be OK as a factory assembly.

Yes thats why i said building wire.

Fixture wire wouldnt work for use as building wire.



There seems to be lots of discussion about what actually qualifies as fixture wires or whips. I know some inspectors here allow #14 in flex up to 6' and some don't. CA is likely to be picky and LA County more picky.
I should have qualified my answer more but when I saw 25', I didn't think it was necessary.

#16 would work for fixture wire inside the fixture but not as building wire in conduit in walls or anywhere other than a fixture.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,592
Location
Fullerton, CA
or anywhere other than a fixture.

1 other electrician and I installed 30 MILES of #16 TFFN Str red in rigid conduit, 18" or less of sealtite on the ends, none bigger than 1/2", as part of a upgrade to the brakes on a computer controlled amusement ride at Knott's Berry Farm. The wires were tagged on the ends to identify them.
The conduit was all threaded (only 1 erickson union used on the installation), and all condulets (no boxes at all). The conduit had to conform to the arcs of the tracks.
It was inspected by the State.
 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
What gauge of wire is used in pre wired whips to run from fixture to junction boxes?
We supply 6ft FMC whips with 18 AWG solid on a regular basis. The difference on this job is we're only supplying the wire, it's 25 ft. long and they want a mate-n-lok connector on the fixture end.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
The only place I am aware of as part of the building wire that is allowed to be undersized is from a switch to a light fixture in a travel trailer. As I recall whips were length limited. I see 18 cord, solid in the fixtures, seems the smallest I see in a whip is 16, similar to an extension cord etc. But,,, this is just gibberish by me.
 