"I thought I read somewhere on here a while back that the neutral was supposed to be switched along with both hots--to prevent a possible backfeed on the neutral. If I misread just disregard this comment."
Grey Owl,
I was originally under this assumption because my experience was w/ a 3-way switch switching the neutral. In addition, intuitively it seemed to be more disconnected from the power grid to switch the neutral. However, I've since learned that my original experience was set-up quite a bit different, and so it's not quite so simple.
As MRB points out, how the generator is bonded makes a world of difference. Honda inverter generators
do not bond the neutral to the frame. As I mentioned this makes a huge difference in how the transfer switch is wired.
I would still prefer to switch the neutral (which has been my experience, and which is the way Canada's CEC code is written) but Honda inverter generators do not allow bonding of the neutral to the case ground. I called the manufacturer and talked w/ a service rep, and they simply do not allow a straightforward way to allow bonding of the neutral to the ground.
As such, per NEC guidelines, I'm stuck w/ running the neutral straight through.
NEC guidelines are well thought out. It can actually be unsafe to switch the neutral on a neutral un-bonded generator.
In another post, I've diagrammed how at least one side of the generator coil can go up through the transformer with an un-bonded generator and a switched neutral (not to say one side of a generator coil will automatically electrocute a lineman, but I'd prefer not to allow even one side of the coil (of the generator) to go up through the transformer).
All that aside, there is still something about this discussion that I don't understand and would use this as an opportunity to learn. To wit:
Schnieder electric has a web page that indicates a 220v generator w/ a floating neutral can have trouble regulating voltage if the transfer switch switches the neutral. In their words:
"These Diagrams show that a 3-pole transfer mechanism switching Line 1, Line 2 and the neutral conductors would result in a circuit that
does not comply with the rules of the CEC. In
stand-by power mode, a circuit exists in which
the system voltage from the generator could
float on each phase. In the most extreme case
240Vac would appear on one phase and 0Vac
on the second phase, potentially resulting in
damage to any 120Vac equipment operated in the home."
For the life of me, I can't understand how the voltage could "float" with an un-bonded neutral along with switched neutral at the transfer switch. Most 220v gen sets simply have two 120v coils that are connected at the middle to form a neutral (much like split-phase 220/110v service). How can one coil in a generator produce 220v, while the other produces 0v, in the example Schnieder electric points out. Any one out there familiar enough with electrical theory to explain this to me?
Here is the link to their page look specifically at the last page:
http://members.rennlist.org/warren/Gen_Panels_Appl_Note_EN.pdf