Hey guys. Ive had this gree mini split unit for approx 2 years. Im wondering if it may be slightly low on charge. Maybe i have a slow leak somewhere? I saw ice build up on this 4 zone heat pump and watched it slowly get worse.
I was expecting the defrost cycle to kick in but it did not. So I checked the service manual.
The outdoor temps were just above the defrost parameter (of below 41*F) it was 42-43* F outside and the unit also needs to see 3 hours comp run time with a coil temp of below 31*.
The outdoor humidity was 73%. I know theyre supposed to frost up but thought this was too much ice so I shut the unit down.
What do you guys think? Im goin to contact my installer and see what he says. It was heating well for a few days prior to this issue.