Hey guys,
I installed a Mitsubishi SLZ/SUZ-KA15NA mini-split setup in my garage a few weeks back, and over the last few days it seems to have started having trouble holding ~75°F. I'm not sure if this is due to the fact that it has started to get even hotter, but as a reference, the current outdoor temp is 88°. The garage is fully insulated (max R13), but there are some small air gaps (haven't installed the molding yet around the exterior door or the attic access). There are minimal air gaps on the garage door itself (about as tight as I've ever seen).
I've gone through all the maintenance menus and found no error faults, etc.
I put the system into "Test Run" mode and after a few minutes, the coolant pipe temp hit a low point of 10°F. After a few minutes, it stabilized at 21°F. Still no error codes. During said test run, the air coming out of the cassette was WAY cooler than it is in normal operation.
Do these things adapt to their environment in order to maximize compressor efficiency? If so, is it possible to reset these adaptations or modify them in any way?
I'm about to check the low-side pressure but would love any input you can give.
Indoor: SLZ-KA15NA
Outdoor: SUZ-KA15NA
Controller: PAR-33MAA
Thanks in advance.
I installed a Mitsubishi SLZ/SUZ-KA15NA mini-split setup in my garage a few weeks back, and over the last few days it seems to have started having trouble holding ~75°F. I'm not sure if this is due to the fact that it has started to get even hotter, but as a reference, the current outdoor temp is 88°. The garage is fully insulated (max R13), but there are some small air gaps (haven't installed the molding yet around the exterior door or the attic access). There are minimal air gaps on the garage door itself (about as tight as I've ever seen).
I've gone through all the maintenance menus and found no error faults, etc.
I put the system into "Test Run" mode and after a few minutes, the coolant pipe temp hit a low point of 10°F. After a few minutes, it stabilized at 21°F. Still no error codes. During said test run, the air coming out of the cassette was WAY cooler than it is in normal operation.
Do these things adapt to their environment in order to maximize compressor efficiency? If so, is it possible to reset these adaptations or modify them in any way?
I'm about to check the low-side pressure but would love any input you can give.
Indoor: SLZ-KA15NA
Outdoor: SUZ-KA15NA
Controller: PAR-33MAA
Thanks in advance.