Mini split install questions/suggestions

jeopardy98

Well-known member
Joined
May 11, 2015
Messages
587
Location
Prince George, VA
I have pretty much decided on a MrCool DIY 2 ton ductless heat pump setup for my garage area. My original plan was to purchase this in about a year so I had the electrician do a run with 10/3 and install a dedicated 30 amp breaker for the mini split. I originally thought I would just run the lineset right out the back into a wall mounted compressor so that I wouldn't have an ugly lineset on my new vinyl siding but now I'm not so sure.

The mini split comes with a 16' lineset which means I will have to coil the set. Also I'm not sure that wall mounting is the best idea at this point. Should I just mount it to a pad? Could I offset the inside and outside unit just enough to coil the lineset inside the sheetrock?

Do I have to have a junction box since the compressor will feed the inside unit and I already have a dedicated breaker? If so since I already paid the electrician to pre-wire for a mini split shouldn't he come back and do that once the siding is on?

Is it okay to run the lineset and drain tube inside the wall? The sheetrock is up but the vinyl is not so I could remove a piece of the exterior sheathing and install the lineset that way.

Am I overthinking this all? Should I just run the lineset down the vinyl and cover it with vinyl gutter protector?

Any and all help from those of you who have done this is appreciated. Comments, suggestions, or concerns are welcome too.
 
To avoid these ads, REGISTER NOW!

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,680
Location
Maine
I have pretty much decided on a MrCool DIY 2 ton ductless heat pump setup for my garage area. My original plan was to purchase this in about a year so I had the electrician do a run with 10/3 and install a dedicated 30 amp breaker for the mini split. I originally thought I would just run the lineset right out the back into a wall mounted compressor so that I wouldn't have an ugly lineset on my new vinyl siding but now I'm not so sure.

The mini split comes with a 16' lineset which means I will have to coil the set. Also I'm not sure that wall mounting is the best idea at this point. Should I just mount it to a pad? Could I offset the inside and outside unit just enough to coil the lineset inside the sheetrock?

Do I have to have a junction box since the compressor will feed the inside unit and I already have a dedicated breaker? If so since I already paid the electrician to pre-wire for a mini split shouldn't he come back and do that once the siding is on?

Is it okay to run the lineset and drain tube inside the wall? The sheetrock is up but the vinyl is not so I could remove a piece of the exterior sheathing and install the lineset that way.

Am I overthinking this all? Should I just run the lineset down the vinyl and cover it with vinyl gutter protector?

Any and all help from those of you who have done this is appreciated. Comments, suggestions, or concerns are welcome too.
You have to have a outdoor disconnect for the outdoor unit. Also for the indoor unit but some places aren't enforcing that.
 

fabjunkie

Well-known member
Joined
Jul 24, 2008
Messages
110
Location
Magnolia, TX
I think I'm leaning towards the MR. Cool DIY 24k myself. Get this for the lineset. Cheaper than Ingrams has them. Amazon has a cheaper wall mount too ($25) but the reviews say that you get about 8" max from the unit to the wall. This may be the same distance as the $59 wall mount from Ingrams. Ingrams looks better and easier to install as well.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Some manufacturers have minimum line lengths, also max but.....

Thats why you adjust the amount of freon in the system.
You need to check the pressure in the system and adjust the amount of freon accordingly,no matter what the length of the lineset.
 
Last edited:

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,680
Location
Maine
Thats why you adjust the amount of freon in the system.
You need to check the pressure in the system and adjust the amount of freon accordingly,no matter what the length of the lineset.
I don't know **** about a Mr cool unit but you charge by weight on the ductless systems I've Been around. But they are variable speed compressors so pressures will depend on load, indoor and outdoor temps.

Not sure I'd want excess line set coiled up but I've heard of it being done
 
OP
J

jeopardy98

Well-known member
Joined
May 11, 2015
Messages
587
Location
Prince George, VA
Thats why you adjust the amount of freon in the system.
You need to check the pressure in the system and adjust the amount of freon accordingly,no matter what the length of the lineset.
This is a complete DIY install. System is precharged and the lines have quick connect fittings. Nothing more than hand tools needed for the install and the warranty remains valid. This is why I don't want to shorten the lineset.
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,680
Location
Maine
This is a complete DIY install. System is precharged and the lines have quick connect fittings. Nothing more than hand tools needed for the install and the warranty remains valid. This is why I don't want to shorten the lineset.
So you don't evacuate line set and indoor unit after install?
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
I don't know **** about a Mr cool unit but you charge by weight on the ductless systems I've Been around. But they are variable speed compressors so pressures will depend on load, indoor and outdoor temps.

Not sure I'd want excess line set coiled up but I've heard of it being done

All condensors are factory charged by weight as a baseline(except dry condensors),But you still have to check the running pressure of the system and adjust things from there.
What do you do when the system is a little low on freon 5 years after its installed?:wtf:
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
This is a complete DIY install. System is precharged and the lines have quick connect fittings. Nothing more than hand tools needed for the install and the warranty remains valid. This is why I don't want to shorten the lineset.

So how do you know the system is running correctly without putting a set of gauges on it and checking the pressures?
 
To avoid these ads, REGISTER NOW!

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,680
Location
Maine
All condensors are factory charged by weight as a baseline(except dry condensors),But you still have to check the running pressure of the system and adjust things from there.
What do you do when the system is a little low on freon 5 years after its installed?:wtf:
You' re supposed to evacuate and weigh it back in, fujitsu, Mitsubishi daiken, these are the ones I'm familiar with
 
Last edited:

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
You' re supposed to evacuate and weigh it back in, fujitsu, Mitsubishi daiken, these are the ones I'm familiar with

This, every mini-split I've seen in recent years has been charge by weight only with an amount given to add per foot for linesets over specified length.

Having a charge port only on the suction line makes it tough as well on a txv system.
 

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,411
Location
N CA
All condensors are factory charged by weight as a baseline(except dry condensors),But you still have to check the running pressure of the system and adjust things from there.
What do you do when the system is a little low on freon 5 years after its installed?:wtf:

You carefully measure and record the installed line set length on the inside of the condensing cover at the line set. In five years if things are low and you need to recharge, the factory service dept will tell you to evacuate the system, triple evacuate, nitrogen purge (oh yeah, find the leak) and weigh in the proper new charge of 410A. Your gauges will tell you when the system is off, but only the scale will tell you when it is right. That is all according to Fujitsu.

If you have extra line-set length, do not "coil" it. Doing so traps oil in the loops. Lay the line set off in a serpentine fashion.
 
OP
J

jeopardy98

Well-known member
Joined
May 11, 2015
Messages
587
Location
Prince George, VA
You carefully measure and record the installed line set length on the inside of the condensing cover at the line set. In five years if things are low and you need to recharge, the factory service dept will tell you to evacuate the system, triple evacuate, nitrogen purge (oh yeah, find the leak) and weigh in the proper new charge of 410A. Your gauges will tell you when the system is off, but only the scale will tell you when it is right. That is all according to Fujitsu.

If you have extra line-set length, do not "coil" it. Doing so traps oil in the loops. Lay the line set off in a serpentine fashion.
Does it matter how many bends there are as long as it isn't "coils"? Is there an advantage to wall mounting vs mounting on a pad? I'm going for a clean install.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,411
Location
N CA
I wall mount all of mine. In my experience it keeps them cleaner, makes it harder for snakes and other critters to get into them, and if using them for heat it is easier for the water to drain off in the defrost mode. Also, the manuf like the condensing units to be level. With frost heave and all they can get knocked around. Roof mounting is good too.
You have to know the manuf spec on line sets. Fujitsu has min and max line set lengths. When ,I have weird routing and worry about kinks, etc I'll strip off the insulation, and slide a spring bender along the tubing making the bends as I go. It can be really hard and frustrating. Number of bends isn't a problem, but I do long radius bends too.
 

fabjunkie

Well-known member
Joined
Jul 24, 2008
Messages
110
Location
Magnolia, TX
OP
J

jeopardy98

Well-known member
Joined
May 11, 2015
Messages
587
Location
Prince George, VA
I'm planning to call tomorrow and ask a few questions. I'm pretty sure that call will end with an order. Going to use a 4" vinyl dryer vent for the exit of the lineset. Wall mount the compressor right where the lineset exits.
 

fastjohnny

Well-known member
Joined
Sep 3, 2011
Messages
261
Location
SW Michigan
If you want this brand, I'd much prefer this unit for better efficiency: http://ingramswaterandair.com/mrcool-premier-seer-ductless-minisplit-heat-pump-p-22730.html
I think you are paying a premium for a less efficient unit due to the precharged lineset and quick connect fittings.
Flaring and evacuating the system is not that difficult, I'd definitely recommend it, that way you are not locked in to a set line length.

I prefer misubishi hyper heat models, but they are more expensive.
 
OP
J

jeopardy98

Well-known member
Joined
May 11, 2015
Messages
587
Location
Prince George, VA
If you want this brand, I'd much prefer this unit for better efficiency: http://ingramswaterandair.com/mrcool-premier-seer-ductless-minisplit-heat-pump-p-22730.html
I think you are paying a premium for a less efficient unit due to the precharged lineset and quick connect fittings.
Flaring and evacuating the system is not that difficult, I'd definitely recommend it, that way you are not locked in to a set line length.

I prefer misubishi hyper heat models, but they are more expensive.

You are probably right but that unit requires a licensed HVAC person to evacuate the system. My guy wants $500 for that. I'm also paying more for the unit and the yearly difference in energy costs is about $75 so it would take me 8-10 years to recoup the cost difference. That unit also has a minimum 16' lineset.
 
OP
J

jeopardy98

Well-known member
Joined
May 11, 2015
Messages
587
Location
Prince George, VA
Just an update. I ordered the 24K DIY unit and it should be here next Wednesday or Thursday. I'll update this thread with some pictures when I install it.
 

justinjoyal

Well-known member
Joined
Apr 30, 2015
Messages
888
Location
Quebec
You carefully measure and record the installed line set length on the inside of the condensing cover at the line set. In five years if things are low and you need to recharge, the factory service dept will tell you to evacuate the system, triple evacuate, nitrogen purge (oh yeah, find the leak) and weigh in the proper new charge of 410A. Your gauges will tell you when the system is off, but only the scale will tell you when it is right. That is all according to Fujitsu.



If you have extra line-set length, do not "coil" it. Doing so traps oil in the loops. Lay the line set off in a serpentine fashion.


The reality is that, if out of warranty, most customers will prefer paying for the call and a little amount of gaz... And you can't really blame them.

If a system has been working fine for 5 years, it means the leak is tiny. A top-off will cost less than 100$ and most likely last them another 5 years...

Evacuating, triple evac, nitro purge, vacuum, charge... It all costs a lot more and from my experience customers can very well live with that tiny leak.
 