Daikin mini split calls for 625 psi nitrogen leak test when new. That is with the service valves closed, so only testing lines and evaporator.
I will need to nitrogen test the condensor after getting the unit evacuated so the service valves will have to be open. The high side design pressure is 604 psi and the low side is 391 psi. So it seems that I should use less than 391 psi, is that correct?? I do not want to put the system on heat to raise pressure as I have no idea how much refrigerant is in the system and do not want to risk damaging unit.
I will need to nitrogen test the condensor after getting the unit evacuated so the service valves will have to be open. The high side design pressure is 604 psi and the low side is 391 psi. So it seems that I should use less than 391 psi, is that correct?? I do not want to put the system on heat to raise pressure as I have no idea how much refrigerant is in the system and do not want to risk damaging unit.